TNCS or TT supply to external metal pressurised plantroom

Hi,

I have been tasked to run a 3phase supply to an external metal container plantroom and the pipework is all in copper feeding back into the building.

The main supply in the switchroom is a TNCS supply.

I am thinking of making the supply to the container a TT system.

I am concerned as the main water pipe is in the building and will be earthed to the MET at the TNCS cablehead. - along with the sprinkler system.

I am wondering if I should just make the supply to the container a TNCS supply with a separate C.P.C as it only about 4 meters away from the main building.

The container will be a fixed to a concrete plinth and will be a permanent structure.

Any advice would be much appreciated.

Regards

Alan