Expected Ze reading on LV adjacent to a 800Kva transformer ?

So I'm trying to work out some cable calcs for a sub main leaving LV Side distribution equipment sited adjacent to a 800Kva transformer , any ideas what the Ze is likely to be  ? I would think it will be really low 

Parents
  • 0.02 Ohms

  • 0.02 would be a bit high - at full load a drop of 1200 A*0.020hm= 24 volts circa 10% - I'd expect  half that or less for the impedance right on the terminals.

    Mike

  • Thanks for the explanation, much appreciated 

  • 0.02 would be a bit high

    But, 0.02 ohms might be the limit of the resolution of the instrument used, i.e. 0.01 ohms (rounded up) plus 1 in the last digit.

    For measurements taken in close proximity to a transformer, a "normal" earth fault loop impedance tester is not always an appropriate instrument to use ... at least to get a "meaningful" reading.

  • In a recent inquiry with the DNO responsible for managing the substations on one of my sites, I obtained the following values for an 800 KVA transformer:
    • Phase L1: 0.01 with a prospective short-circuit current of 20 kA
    • Phase L2: 0.02 with a prospective short-circuit current of 15.1kA
    • Phase L3: 0.01 with a prospective short-circuit current of 20 kA

  • With an 800 kVA transformer, I would have thought this would have been provided with an anticipated reactive component or phase angle to be of any real value (similarly, prospective fault current). Having said that, it's usually possible to develop these from a standard-type transformer model.

  • Just to be clear. I only asked for Ze values for a particular substation with a 800kVA transformer 

  • or measurements taken in close proximity to a transformer, a "normal" earth fault loop impedance tester is not always an appropriate instrument to use ... at least to get a "meaningful" reading.

    Absolutely - as per a recent post about measuring low value resistances on earth clamps, beyond a certain point  the reading eventually becomes a report of the instrument test leads and internal wiring - higher test currents and corrections for leads and probe/connection resistances are needed if it really matters.

    If such a 'fruit machine' reading  matters in practice or not rather depends on what the resulting figure is used for - for ensuring that the death or glory fuse will blow reliably, impedance just needs to be low enough, and not so low that when the fuse blows it does so so energetically that it takes something with it. The sort of fuses that should be used would normally energy limit, so the rating of switchgear and breakers further down stream is probably set by the choice of that first fuse, rather than just the transformer itself.

    Mike.

  • Just to be clear. I only asked for Ze values for a particular substation with a 800kVA transformer 

    Understood.

    "Z" has two components - resistive and reactive. Whilst it might be OK to provide 100 A supply Ze and assume x is approximately zero, It's not really a suitable answer to provide a "Ze" values for that size of supply in terms of resistance (or "magnitude") only.

  • Interesting - being quoted to one significant figure, suggests it is test resolution limited, then all 3 resistances could be very different or all the same really in the sense that

    (0,01+/- 0.01) means anything between 0.00 and 0.02

    (0,02+/- 0.01) means anything between 0.01 and 0.03

    A finer instrument would have been useful (0.011 perhaps)

    the apparent  precision of the 15kA is probably an illusion, as that current is only calculated from the measured resistance.

    Still, interesting, as it does imply rather a large volt drop at full load, hopefully inductive, or the transformer will need  fan set to sweat it off it it is resistive loss ;-)

    Mike

Reply
  • Interesting - being quoted to one significant figure, suggests it is test resolution limited, then all 3 resistances could be very different or all the same really in the sense that

    (0,01+/- 0.01) means anything between 0.00 and 0.02

    (0,02+/- 0.01) means anything between 0.01 and 0.03

    A finer instrument would have been useful (0.011 perhaps)

    the apparent  precision of the 15kA is probably an illusion, as that current is only calculated from the measured resistance.

    Still, interesting, as it does imply rather a large volt drop at full load, hopefully inductive, or the transformer will need  fan set to sweat it off it it is resistive loss ;-)

    Mike