Charging box Sales ban in Sweden for Non compliance to EU standards
I was going through the news of Swedish authorities “Elsalerhetverket” imposing a Ban on Easee chargers recently.
Easee is a renown Norwegian EVSE company with almost 100000 installations of EVSE in Sweden alone.
https://www.electrive.com/2023/03/15/elsalerhetverket-imposes-sales-ban-on-easee-wall-boxes-in-sweden/
 According to a ten-page letter from the Swedish supervisory authority Elsälerhetverket to Easee it is mentioned
"Contrary to the declaration, apparently no FI switch installed" - and this increases the risk of fire. In addition, some EU declarations are said not to have been fulfilled, which could also have an impact in other countries. There are several allegations that affect the safety of the product. The main accusation: "The operating instructions state that the product has a built-in FI circuit breaker. The product is not equipped with an earth leakage circuit breaker (30mA AC/6mA DC) as indicated in the instructions for use". So: "The instructions do not mention that the product must be preceded by a residual current circuit breaker if it is to be connected to the fixed network."
According to electrive.net, there are  “additional defects that go beyond the defects identified in the previous tests and investigations by the electrical safety authority. In addition to the lack of proof of the function of the RCD and DC protection, the product fails the overvoltage test LLLN->CP, which is a serious defect have also complained about "complete instructions for use".
According to Elsäkerhetsverket , the company stated in its EU declaration of conformity that the product conforms to the standards, but the opposite is the case. The product must meet all the requirements of the standards and not just selected parts. In addition, it was noticed during the examination that the labeling defects now listed had already been criticized in June 2021. This can have bad consequences. If the company cannot refute or eliminate the allegations, the worst that can happen is a sales ban.
Most of the EVSE use the technique similar to Easee with RDC-DD inside the EVSE tripping the main relay.
There is a lot of confusion with this? can anyone clarify on the above issue?
  • Seems similar to the ICS charger I was talking about a few days ago.
  • Does anyone know which standard this test clause "Overvoltage test 7000V towards PELV (LLLN->CP)"  comes from?
  • Not sure about the 7000V bit, but the report seems to suggest that it's IEC 61851-1 (a.k.a. BS EN IEC 61851-1) that calls for it to be SELV/PELV. Unfortunately I don't have access to the standard to verify that though. Often technical details are picked up from other standards - so it might only say something like 'according to the requirements of ... (some other standard)' rather than quoting numbers directly.
  • The makers response, now on the web
    https://www.dagbladet.no/files/2023/02/15/22EV1261%20%E2%80%93%20Response%20letter%20from%20Easee%20AS.pdf
    also makes interesting reading. The 7kV  seems to be part of  an impulse test, and the argument is that the pilot conductor is not an accessible PELV part , and so the test does not apply.
  • It looks we nteed to wait until after 24. July to get an answer on that. The 44. July is the deadline that the Elsäkerhetsverket have to answer on the answer from Easee.
  • Thanks for that Mike - it makes interesting reading. I didn't see any obvious mention of the relay contact separation distance though (for overvoltage) or breaking capacity.