Luton Airport Car Park Fire
The car park fire is now in the clean up phase.
It does not seem good that a 3 year old car park which apparently met the requirements could burn so catastrophically. There was a similar fire in Liverpool in 2017. The official fire report raises a number of issues and questions.
https://www.bafsa.org.uk/wp-content/uploads/bsk-pdf-manager/2018/12/Merseyside-FRS-Car-Park-Report.pdf
To me the key point in the Liverpool fire was the spread of fuel due to the failure of plastic fuel tanks compounded by the drainage system.
Would requiring sprinklers help? Would sprinklers make an EV fire worse?
  • ICE or EV or Hybrid vehicle may have started the fire but the chain reaction that destroyed over 1000 vehicles (and by my understanding they are going to demolition the whole structure for safety reasons) also needs to be looked at.
    It would be good to see what they had for a fire risk assessment for that car park, considering it was only built a few years ago(I think 3 years).  Was there any consideration for a EV catching fire while charging or not charging but suffering from thermal runaway.  What about a fire in close proximity to an EV.  At this point people will say that an ICE needs the same risk assessment but we have no issue with a metal can on our driveway with 70 litre of fuel in it.  (Which is a valid point)
    However I have seen ICE vehicle fires and I have seen them put out quite quick and easy.  EV fires on the other hand are not the same beast.  Another point to consider is that when the vehicle is on fire for whatever reason how long before it spreads to the next vehicle.  I have seen this demonstrated with mobile phone batteries.  1 was punctured and left to ignite and the fire was like the back end of a firework.  In the second test they punctured the same make and model battery and placed it 10cm from another battery and then 10cm another battery was positioned.  The result was truly scary.
    In both tests the first battery caught fire and burned vigorously but in the second test the adjacent batteries also caught fire and when they did the heat and intensity of the fire area grew.  Now imagine 10 EV cars lined up together and one catches fire and is burning so intense that it makes the next vehicle catch fire.  The domino effect of each successive car catching fire means more work for the attending fire fire-fighters.
  • It was definitely a standard diesel car. One of the firefighters present that evening is an acquaintance of mine. Slight smile
  • The report has now been released:
    London Luton Airport: Car Park 2 Incident Review | Bedfordshire Fire and Rescue Service (bedsfire.gov.uk)
    Luton Airport car park fire could have been limited by sprinklers - report (bbc.com)
    A sprinkler system could have changed or limited the huge multi-storey car park fire at London Luton Airport, according to a new report.
    Bedfordshire Fire & Rescue Service (BFRS) has published a significant incident report into the blaze on 10 October 2023 which was tackled by more than 100 firefighters at its peak.
    The fire started in a diesel vehicle on the third flood of Car Park 2, but because of wind blowing through the open-sided structure it spread quickly and destroyed 1,352 vehicles and caused a partial collapse of building.
    Investigators said although a sprinkler system was not mandatory for an open-sided multi-storeys, it would have "changed and delayed the pattern of fire spread".
  • Thanks for sharing this Roger. Makes interesting reading. Slight smile
    Would love to know who this person was and whether or not they were reprimanded for not only putting their own life at risk but the lives of the rescue crew as well:
    "During this second phase an individual was spotted in Car Park 2 and was rescued. The individual worked in the terminal building (but was not an employee of LLAOL) and had entered the building approximately one hour after the start of the incident and had used their status as an airport worker to gain access to the building in an attempt to remove their car."
    Flushed
  • Modern compliance does not guarantee real fire safety, as shown in the Merseyside car park fire. Fuel spread from ruptured tanks and drainage contributed significantly. Sprinklers can limit liquid fuel fires if properly designed, but EV battery fires behave differently and require a performance-based evaluation of suppression effectiveness.
  • Merseyside car park fire.
    While doing the classic internet research, I also found ‘Lessons not learnt’ from multi-storey car park fires from the Institute of Civil Engineers. And so it goes on..