AJJewsbury:
Im presuming though that its about ensuring compliance with the standard in force at the time it was made up, not the latest (when altering things)
That sounds sensible, but if my reading of 536.4.203 is correct, I think the actual wording of the requirement is to meet the current BS EN 61439 series ... so my implication including those to earlier (possibly incompatible) standards. Doesn't sound too practical does it?
Zoomup:
mapj1:
About 5 years ago I wanted a C type RCBO for a Volex board, and they did not seem to make them.
However, I rang them up to check and was told that, no they didn't but all their MCBs and so forth used the same internals and metalwork as the Wylex ones, only using a cheaper printed plastic process, and that it would be fine to fit the Wylex one.
And indeed it fitted perfectly, and as far as I know it is still in service. If I'd known it would be useful, I'd have asked for it in writing.
...They are all interchangeable.
psychicwarrior:
My question and I am just trying to understand the technical and regulatory issues here: is it not possible at all, to issue a MEIWC to current Regs as a result of putting in a different branded RCBO (I cannot re-do the type testing etc of course!) and where might/is that prohibition backed up in the 'frustrating' Regs Book please ?
Although we do supply all our components as separate items on our invoice, we can and do ship the the components already assembled, if you wish us to, at no extra cost. Where the resulting Distribution Board, as designed by you, is not certified to BSEN61439-3, it should comply with BS7671:2008, AMD3, 421.1.201 and/or 133.1.3.
Which I read as ' you decided what to put in it, so it is your responsibility'.
And of course it will be fine in practice, and even if it wasn't it is not non compliance with some EU standard that matters, but the fact it has burnt the wall paper or whatever.
because from what you say it seems to imply that if any work is done then everything must be brought up to current Regs
AJJewsbury:
I don't think it's quite as bad as that - by my reading at least it's only when you're adding devices not specified by the original assembly manufacturer - if you could find an MCB that was officially compatible then you're fine (and the assembly only needs to remain compliant with its original standard). As I read it it's just saying that if you add in "wrong" devices today, you need to ensure that the overall result complies with today's standards.