mapj1:
You are correct, if you are interested in touch voltage between the ground outside, and the CPC of the circuit in question.
But unless you have arms like Mr Tickle, or have a bare earthen floor, then this is not the common indoor case - the common case is the victim simultaneously touching CPC of the circuit and also some internal metal that almost incidentally brings something close to the outdoor ground voltage to somewhere within reach, say the bath taps or the gas pipe to the central heating.
IF there is no bonding from MET to the metallic services, the touch voltage would be as you calculate. But with main bonding, the voltage on these objects gets pulled up during fault, so something near the MET voltage, so the voltage across the victim is reduced, often significantly.
mapj1:
yes, but it is non-text book, being harder ?
If we take your figures for the indoor wiring then the main bonding alone does not on its own do much for you, and supplementary is more use.
If = Uo/Zs
Assume Zs is 0.75 ohms from (Ze - 0.1) (R1 is 0.3) (R2a is 0.3) (R2b is 0.05)
With the fault current of 300 A flowing, the MET rises by 0.05 *300 15V
but the remaining 215V are shared between R1 and R2, so the point of fault is 107v above the MET and any main bonded pipework, and 115 above any unbonded plumbing so not so useful on its own.
Does Ze not drop voltage ? Do we only include R1 & R2?
Think of the metal services as in parallel with R2B.
Redo that with a 10m shower circuit in 10mmsq so R1 * R2A are lower (about 18 milliohms each), or on TNS with R2B that could be 0.5 ohm and then main bonding helps more , but for now lets stick with your figures. You need an RCD to get the power off fast if the exposed voltage is this high, as the idea is to be off in half a heartbeat, and avoid the onset of fibrillation.
Or consider a fault not at the load end, but near the consumer unit, so the main drop is accross R2B, and main bonding helps.
In your case, with a long thin final circuit ( 300milliohms is 15-20m of 1mmsq, or more like 40-50m of 2.5mmsq, or the far point of a very long ring etc ) if we did not have the fast ADS, then we would really benefit from the old style bathroom bonding that went out when the 17th came in, where the CPC of the shower, the bathroom light etc all bonded to each other and to the bathroom radiators and to the bath taps. Now we are adding several lengths of 15mm copper tube in parallel with the R2a - and as 15mm tube is about 30mm2 cross-section equivalent, so 16-18milliohms per 30m length we are now winning quite a bit.