MHRestorations:
... imagine a row of sockets on an RFC... his method would have you cutting the cables at each box and jointing them?
... not proper surface conduit work, where he agreed that no cutting would be necessary as you can unthread and rethread the cables
whjohnson:
There could be something related to the bad old practise of running cables through luminaires to other fittings. A real pain if you need to change the fitting.
Yes - I'd agree that is not a great practice, but it is not forbidden.
AJJewsbury:
Yes - I'd agree that is not a great practice, but it is not forbidden.
Actually, for luminaires, it is forbidden (unless the fitting is specifically designed for through wiring) - reg 559.5.3.1.
- Andy.