John Peckham:
Contrary to common belief supplementary protective equipotential bonding is still required in bathrooms, see Regulation 7091.415.2.
However it may be omitted IF where all 3 of the conditions set out in 701.415.2 are met. And where necessary a test has been carried out to prove compliance with 415.2.2.
The big question is can you omit the supplementary bonding in the "location" (the bathroom) if there is no main bonding as it is not required?
Legh Richardson:
"people used to do that (including things like window frames) and a myth has come about that the 15th required bonding everything"
They did. It was standard practice in the 70s and 80s to Equipotentially Bond the Crittle window frames that were fitted in prefabricated houses as the supporting studding was fixed into the ground floor and the ceiling.