Plastic consumer units/enclosures etc

I have a job where a small former outside toilet is being converted into a hobby pottery complete with water supply and small kiln.

I propose to fit a small plastic consumer unit with the appropriate IP rating for protection against ingress of water.

This will be a home brew job with a generic enclosure and a RCD main switch and mcbs from my spares stock.

I have seen many metal enclosures rusting quietly away in detached garages/w/shops/outbuildings and thought they would be better served by using plastic.


I think there is still a case to be made for fitting plastic consumer unit enclosures in outbuildings in order to prevent deteriation caused by external influences. Moist atmosphere, unheated spaces and the like.


Any other like-minded souls out there?

Comments welcome.
  • I have taken a call from a prospective customer this morning, the meter operative declined to replace the existing meter until the DNO had been out to replace the intake equipment,  that's been done,  so the meter has been replaced,  but both the DNO guy and the meter operative have told the customer he now needs an electrician to install a main earth and tidy things up.


    So it needs three people to tidy the intake, meter and the customers connections to them up.


    Andy Betteridge
  • Alan,

    Thank you for your input.

    I gather that you are situated off the mainland?

    I can tell you that much as can be discerned through direct experience of such matters, the system here does not work as you describe.
  • “there is no proactive maintenance regime in place for the regular inspection of a suppliers equipment.”

    That is a question for the appropriate DNO / Meter Operator. We have a regime in place, allied to meter readings, and will still have a regime in place once smart meters are installed. 


    “Smart meters may well tell tales, but they won't cure a loose and overheating connection inside the meter itself, nor the cutout.”

    No, but it should show if there is a problem, whether the issue is related to the meter installation (which would be concerning), or the butchering of seals by others. 


    “Add to this the confusion as to who exactly is responsible for such equipment” 

    There is no confusion in the legislation. The DNO owns the cutout, the Meter Operator owns the meter. The DNOs have given Meter Operator staff training on removing and replacing cutout fuses and seals, and may do so on behalf of the DNO. 


    Regards,


    Alan.
  • The thing is Alan, as far as I am aware, there is no proactive maintenance regime in place for the regular inspection of a suppliers equipment.

    Smart meters may well tell tales, but they won't cure a loose and overheating connection inside the meter itself, nor the cutout.

    The simplest cure-all when it comes to minimising interfering with meters is the fitting of a simple £10 isolator, then there's no excuse, and the switch provides a single point of isolation for all to use.

    Add to this the confusion as to who exactly is responsible for such equipment and it is a recipe for blame deflection which ends up going round in perpetual circles, with regular choruses of "Not ours mate, not ours".

    How does that assist the consumer and the likes of the LFB when it comes to fire prevention and locating the root cause of a fire?

  • whjohnson:

    . . . Was there no evidence available as to how many badly maintained supply intakes had been the root cause of at least some of these fires? . . . 




    If the DNO / Meter Operator can prove there was not an official seal on the cutout and / or metering equipment at the time of the incident, then the liability will not be with the DNO / Meter Operator In most scenarios. This should improve with the installation of Smart Meters for two main reasons: 


    • It has (or should have) given the opportunity to ensure that every installation was sealed correctly, as every installation has to be visited as part of the project. 

    • “Supply Fail” and “Meter Terminal Cover Removed” are just two of the standard alarms sent by every smart meter. As the smart meter was sealed correctly on installation, these alarms can give clues to interference with the cutout and / or metering equipment, which the DNO / Meter Operator should be following up. 



    Regards,


    Alan.
  • In the model form, in the section "Details of departures from BS 7671", it has "Details of permitted exceptions (Regulation 411.3.3). Where applicable, a suitable risk assessment(s) must be attached to this Certificate".


    411.3.3 is about needing a risk assessment for omitting an RCD.

  • Also, why has a heading entitled 'Risk Assessment Y/N appeared on the forms?



    Where's that? (and is that on BS 7671 forms, or some club's bespoke ones?)


    I might guess it's asking about the risk assessment that's need to omit 30mA RCD protection from socket outlets by 411.3.3 - but that that's a complete guess and could be way out...


      - Andy.
  • Further to my last,

    Lawyers and the threats of litigation should not be permitted to dictate how the laws of physics are applied!

    Therin lies the rub. It is as if the whole pyramid of responsibility is being inverted whereby the Little Man is at the pointy end and being made responsible for items and activities way beyond his control.

    Take for example, the requirement to report upon the state of the DNO's equipment when issuing certification. Why did the IET allow this?

    The certification requests information on the type and rating of the main supply fuse(s), yet this information can only be obtained by breaking the cut-out seals (and potentially the law), withdrawing the fuse and copying down the details.

    Also, why has a heading entitled 'Risk Assessment Y/N appeared on the forms? Risk assess what exactly? Continued use of the installation as is?

    Sorry if I am on a rant,
  • Indeed, and if the fires and accidents remain at comparable rates even after the change of CU, that would indicate perhaps we should look at other variations such as meter tail terminations and other measures.

  • There will be plenty of comparison data from other countries as almost nowhere else on the planet considers a plastic enclosure for electricity to be a bad idea.



    On the other hand, not many other countries try stuffing 7-strand 25mm² into shallow cage clamp terminals or draw up to 100A/phase for domestics.

     

    Use a BG consumer unit with an IP rated aluminium enclosure. 



    Interesting - is that a CU with an aluminium case, or a plastic CU in an additional aluminium enclosure? Either way, it seems a little suspect - aluminium has a much lower melting point than steel (I've melted drinks cans in a simple bonfire - steel food cans survive pretty much intact) - and BS 7671 only reference to the required performance is to ferrous metal.


    at the request of the London Fire Service who made their case to JPEL due to the number of fires they were attending involving consumer units. 



    I still wonder if it might have been more appropriate to lobby the committee behind BS EN 61439 rather than BS 7671.


       - Andy.