Is there any issue with installing a TN ring circuit in hospital operating theatre?
I appreciate Medical IT circuits are in a radial wiring pattern and ultimately any medical equipment is plugged into these circuits, but i'm talking about the 2 /3 TSSO's in the space that are for PC use?
Within BS 7671 clause 710.415.2.3 which talks about earthing there is a note which states:- It is recommended that radial wiring patterns are used to avoid ‘earth loops’ that may exacerbate electromagnetic disturbances.
My question is do these TN circuits need to follow this radial pattern or can ring mains be installed?
Matt