Just what is the shock risk at these two switch positions? What is the likelihood of the metal plates becoming live due to a fault? Has anyone every seen a metal plate switch break down so that the plates becomes live?
Has anyone every seen a metal plate switch break down so that the plates becomes live?
We have a strange relationship with risk of electric shock. All over my house we have exposed live parts hanging out of the ceiling and sitting on top of bed side tables, well at least they are when the lamps are removed.
Zoomup:
Just what is the shock risk at these two switch positions? What is the likelihood of the metal plates becoming live due to a fault? Has anyone every seen a metal plate switch break down so that the plates becomes live?
Z.
Chris Pearson:
Zoomup:
Just what is the shock risk at these two switch positions? What is the likelihood of the metal plates becoming live due to a fault? Has anyone every seen a metal plate switch break down so that the plates becomes live?That the line conductor is loose and comes into contact with the metal. If the switch has a metal toggle, that the toggle becomes live. A CPC would allow ADS to operate. Otherwise you would be relying upon the RCD to trip when somebody touches the switch.
With one fault to danger, I would say C2. With a non-metallic switch, just a C3.