One may also wonder why this cable got hot and burned up its insulation. This will certainly be due to a loose connection, and probably a screw left loose or very low clamp pressure. Crimp connections are much more reliable than screws, provided the correct crimp and crimp tool is used.
Zoomup:
AJJewsbury:
There is a world of difference in a 40 Amp. shower load and a lighting load of a few L.E.D. lamps Andy, as well you know. The possible heating effects are totally different. You are cross threaded. There is no way that the lighting cables could contact the metal light switch plate insulted or uninsulated due to physical separation.
You never mentioned the the lighting circuit for that metal switch was dedicated to just a few LED fittings
You never asked. Just how may lights would you expect a light switch to operate in a small refurbished flat?
Z.
In this article they nod to the issue of interpretation of accessible.
Farmboy:
Chris Pearson:
As for the use of screw terminal as opposed to (MF) junction blocks - are the latter available for greater than 6 mm2 cable; and if so, are the enclosures rated for the current?
So you may be stuck with traditional junction boxes.Are crimps and voltage rated heat shrink not acceptable?
F
AJJewsbury:
There is a world of difference in a 40 Amp. shower load and a lighting load of a few L.E.D. lamps Andy, as well you know. The possible heating effects are totally different. You are cross threaded. There is no way that the lighting cables could contact the metal light switch plate insulted or uninsulated due to physical separation.
You never mentioned the the lighting circuit for that metal switch was dedicated to just a few LED fittings
Chris Pearson:
AJJewsbury:
I asked the NIC about a screw joint box under fitted carpet and was told that could not reasonably be considered accessible.
If you asked me, I'd say that if you gained access to the location to install the JB in the first place, it can hardly be regarded as inaccessible. Of course, things might change in the future - being tiled over or covered with glued laminate - but that's a slightly different question.I tend to concur. It's a pain in the bottom, especially if the boards are T&G, but isn't lifting boards part of the deal?
IIRC, there was an article in https://professional-electrician.com by somebody from Wago which argued that under the floorboards is not inaccessible.
If, however, the sub-floor is sheets of board glued into place, followed by wet under floor heating, and then more boards, perhaps with a decorative or durable finish, nobody is ever going to go through that. Under those circumstances, I have made it clear that should any attention be necessary (presumably not with (MF) equipment) the only way in will be through the ceilings.
Chris Pearson:
As for the use of screw terminal as opposed to (MF) junction blocks - are the latter available for greater than 6 mm2 cable; and if so, are the enclosures rated for the current?
So you may be stuck with traditional junction boxes.
Sparkingchip:
Farmboy:
AJJewsbury:
Fitted carpets are easily removed...?... a matter of judgement I guess as to what accessible / inaccessible is - a homeowner who doesn't want their fitted carpet pulled up may disagree with you, and it's existence may get lost in the mist of time, particularly if the owner moves, but perhaps a notice at the CU may suffice.
F
You offer them the alternative, plastic minitrunking run up, across and back down the wall.
Andy B.