This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Flakey 16mm sub main

It's a 70's property, TT, extended in 2011. They obviously took one look at the ancient Wylex fuse board and decided to split the tails in a Henley and run a 16mm t&e sub main into a new split board supplying the extension.

The water and gas bonds 10mm, yet to be verified, go into the extension board and I've been asked to replace the original board. British gas have installed two new rods (600mm apart?!).

So, the way in which the sub main is installed is non compliant, exposed cores etc, and in my opinion the tails should be split into a switch fuse and the 16mm run from there. I'm thinking that RCD protection can be omitted as the 16mm runs in stud walls and under the floor.

This is an ugly job and I don't like it but I don't want my prejudices to incur additional cost for the client. So am I right in thinking that the 6mm cpc in the t&e is sufficient for the earthing and bonding for the replacement board (as it's TT) and can I just replace the old Wylex board and leave the flakey sub main as is?

Furthermore, if the 16mm t&e did run <50mm and required RCD then how would that work? Is the answer don't run t&e in those circumstances?

  • Sorry to resurrect this thread but I just want to thank Sparkingchip for his PM. For some reason our wonderful new forum software won't let me reply (hello Lisa!).
  • I have the Electrifix special offer flyer in front of me, there goes not seem to be a Type A RCD in sight.


    Andy B

  • Grumpy:

    Sorry to resurrect this thread but I just want to thank Sparkingchip for his PM. For some reason our wonderful new forum software won't let me reply (hello Lisa!).




    I used one of those Type A 300 mA RCDs to replace an upfront RCD which tripped everytime a customers direct drive washing machine was turned on.


    Andy Betteridge 


  • Sparkingchip for his PM. For some reason our wonderful new forum software won't let me reply




    Possibly that is because Sparkingchips options are set to not accept Private Messages


  • Lol.


    I thought the message service was just to tell you if you have a new badge!


    Andy B.
  • Well in your case I imagine it does not look like this (my settings)

    Once turned on you are open to the undercurrent of private messaging, assuming anyone wants to talk to you.

    I do not get the junk mails  about "badges" anymore, that is under the 'notifications' tab.

    realise that 'anyone can see your profile' only means folk who are logged in, which as

    I am mostly out unless I wish to post, has tripped me up.

    .f3d2d9b19a74eb785912474d35bd6a8a-huge-pm-enable.png