Power Cables and CAT6
A friend is looking to get both power and internet into an out building.  Rather than overhead the internet via external grade CAT5 or CAT6, I said, what about using armoured CAT5 or CAT6 underground?  His response then being, can I pull both power and CAT5/CAT6 through the same underground duct?  It would be about 10 metres.
To me sounds unwise, so would appreciate comments.
Many thanks.
Clive
  • Un-armoured network cable, like  bare   telephone cable, needs proper segregation.
    The really nice thing about the armoured stuff is that it brings its own earthed metallic enclosure with it, assuming you install it correctly. Not as much hassle as running it in steel conduit, but from both an EMC and an ADS perspective, pretty much as good.
  • Ordinary CAT 5 and CAT 6 cable, like T&E and PVC flex, isn't necessarily waterproof.
    If you pop them in ducts, and they become submerged for a couple of days, they might just not work.
    External cables are available for this purpose.
    In terms of the networking equipment itself, even just popping a few metres down the garden to an outbuilding might just pop anything on the network in a surge event - I know a lot of people this has happened to at home. Perhaps this is OK if the cost of stuff attached to the network is relatively inexpensive, but SPDs might, of course, help.
    Echo the segregation recommendations, noting that separate ducts are usually recommended for data.
  • I ran in a few hundred metres of Cat 6 cable for a customer and made the glands off a long run of Cat 5 SWA run underground to the electric gates for the audio visual intercom and to operate them.
    The Cat 5 SWA was gel filled and I needed the wet wipes and roll of blue paper towel to hand as I worked.
    I only did the donkey work, a satellite tv guy came to get everything working.
    Andy Betteridge
  • Sparkingchip:
    http://www.doncastercables.com/cables/17/77/EV-Ultra/Power-and-data-connectivity-combined-in-one-cable/
    Seems that it comes in both 4mm2 and 6mm2 sizes, both either Tuf-Sheath or SWA  in CAT5 4-pair or a single-pair for I guess 4-20mA  analogue or 20mA loop* or other data applications. (* is 20mA current loop still used? Seems it is good for 600 metres at 19.2kbps or much further at lower data rates. Brings back memories of the ASR 33 teletype....)
    Clive
  • Eddie Currents:
    Probably stating the obvious here and you have considered this but maybe the internet connection could be provided using a WIFI Extender ie TP Link as it's only 10m away.
    Just a thought Clive
    This method has a greater time delay (latency) over direct wiring; OK if you accept that..
    Jaymack