davezawadi:
I think that there is a serious problem lying hidden here. I do not like disconnecting anything for a periodic inspection ...
Chris Pearson:
davezawadi:
I think that there is a serious problem lying hidden here. I do not like disconnecting anything for a periodic inspection ...
Quite right too - 651.2 "Periodic inspection shall be carried out without dismantling, or with partial dismantling, as required."
The more you dismantle, the further away you get from the installation as is.
Any comments on my point about about testing circuits with SRCDs or USBs which have to be disconnected?
Zoomup:
Chris Pearson:
davezawadi:
I think that there is a serious problem lying hidden here. I do not like disconnecting anything for a periodic inspection ...
Quite right too - 651.2 "Periodic inspection shall be carried out without dismantling, or with partial dismantling, as required."
The more you dismantle, the further away you get from the installation as is.
Any comments on my point about about testing circuits with SRCDs or USBs which have to be disconnected?
There are no two ways about it. If you wish to test insulation resistance of fixed wiring at 500 Volts then all loads and every other item that may affect the results or that may be damaged by the testing has to be disconnected. Years ago this just meant turning off fixed appliances by the double pole switch, removing lamps and unplugging appliances at sockets. Nowadays it is more complicated than just a forgotten door bell transformer still connected to a lighting circuit in the loft.