Torque settings
Hi all,
Obviously, where available we use manufacturer's torque settings for connections. But where do they get them from?
I ask this not least because it's not always easy to obtain, at least in a timely fashion, but also because I appear to have conflicting instructions on some OEM'd equipment (comparing the original manufacturer with the wrapped supplier) or notably different settings when using the same lug onto a very similar terminal bar from a different supplier. It would also be helpful to be able to sense-check the answers for misplaced decimal points.
Jam
  • M10 and 60 Nm - that needs to be a high tensile bolt!
    Another consideration, at least at the smaller end of things is the type of screw head. With slot or cross-head, one has to be very careful that the driver does not slip, and even worse, chamble the head. Hex slot better, Torx better still.
  • Precisely! Hence thinking it'd be nice to have a feel for how it might have been arrived at and not to just follow blindly.
  • The other problem is that torque on the shaft and the compression force on the things being clamped are not simply related - you might like to think that the thread ramp angle would convert one to the other but the whole point about threads that are not intended to be worm drives, is that the friction on the thread resisting turning is the dominant term, not the unwinding forces.
    (mathematically a thread is just an inclined plane wrapped around a stick...)
    So, it depends on the surface finish of the threads in the nut and bolt part, more than anything else.  So the torque to get the thing undone is far from being equal and opposite to the forces originally required to do  it up.
    We sort of know this, as an extreme case of rough thread surfaces, when replacing the exhaust pipe on the car, the nut can be completely off load such that the pipe rattles and the joint leaks,  and yet the thing is corroded enough that it still needs several gorrilla-feet of torque to get it to budge, and then only with an awful teeth jarring graunching squeak, or in some cases it is still energetically favourable  to snap the stud off short in the block,  rather than undo the thing, then requiring some cunning with the welder to get it out...
    The related effect is that you can clamp a copper wire in a terminal to limit torque, and then warm it and cool it and the thing strains when warm and relaxes when cold, the copper shifts about a bit and afterwards the bolt can be almost any torque, right down to  finger loose.
    I'm a great believer in fitting methods with a bit of spring to them (crimps on strands or star washers on bolted lugs and similar) to take up the slack in thermal cycling, but on a normal terminal block, there is no 'stretchy' element, I do not think the bolts compress very much, and only on a cheap one does the terminal tunnel deform, and then it is not reversible.
  • a thread is just an inclined plane wrapped around a stick...  engineers sometimes use the phrase "A helical projection on a cylindrical bar"
  • The answer to this is always "very tight". The manufacturers figures are really quite high if you have a torque wrench or similar, and the average person leaves things too loose. You may have noticed that all the CU screws these days are not brass as of yore, but zinc plated steel, as are the neutral and earth bars. This is to make the torques sufficiently high that thermal expansion never removes all the preload from the screw. BTW 60nM and an M10 grade 8 HT bolt is quite small, it will stand at least 200 nM (that is a 20kg push on a 1 metre long spanner, so easily done). I have a 650 nM air impact wrench which will sometimes just break M10 (rusty) bolts, which is sometimes a useful dismantling technique if they have nuts as through fixings, or on old exhausts it saves getting the oxy gas out.
  • davezawadi:
    I agree that many are surprised how tight the manufacturer's figures are. For example, if you ask even an experienced assembler (but not used to working in an environment that routinely uses torques such aerospace, medical, ATEX etc) to tighten up say a typical Weidmuller WDU terminal, then get them to do it again to the specified torque, most are surprised at the difference. It is important to use good quality drivers of exactly the right size or it easy to damage the screw head.
    edit: of course you get the odd gorilla and then the specified torque is there to stop them over-tightening.
  • davezawadi:
    Or just virgin tight. ?
  • The comment about the zinc plated steel bolts brings to mind an accident I've had once or twice... you go round doing the 'check all connections INCLUDING factory ones' routine before closing the CU cover on a new install or indeed any job... get used to the way the torque feels... then proceed to tear off the head of a screw in the external Main Earth Terminal block, because they're still brass... D'OH!
  • Bolts, bus-bars and stuff technical issues.......
    https://books.google.co.uk/books?id=EkStW7v8VPkC&pg=PA233&lpg=PA233&dq=youtube+electrical++bus+bar+bolts&source=bl&ots=FseR5mv_un&sig=ACfU3U32KSb83_soBCP27mzSsNMxne1S2Q&hl=en&sa=X&ved=2ahUKEwibmpXz8J7nAhX1olwKHUx2Cvw4ChDoATABegQIChAB#v=onepage&q&f=false
  • Zoomup:
    Ooh interesting, thanks Zoom. Sadly the IET's libary copy is reported as missing (give it back whoever you are), so this might be an expensive week.
    @mapj1‍ That's helpful. To the first approximation, then, the manufacturer is not terribly worried about the spec of the lug palm or the bar (to be fair this is also apparent retrospectively from Chris Pearson's link and others, but spelling it out has helped). Which is good to know when selecting fittings. But their nut and bolt should be used, or more to the point replaced like for like if not available for any reason... and if not provided we should be asking for a precise specification including bulk material and finish.
    Everyone else - thanks again for the interesting conversation.