gkenyon:
weirdbeard:
Hi John, BS 7288 wasn't listed in appendix 1 of the 2008 17th edition, and here is a related topic from ye old forum:
https://www2.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=28346
Would you mind explaining why this has fairly recently become an issue that you hold dearly? ps, you seem to be struggling to get your new board fitted, I have a couple of hours spare next week if you need any help :)
BS 7288 itself has been updated.
The current version of BS 7288 does not have the same provisions as the previous version, and, in addition, attempts, perhaps somewhat clumsily, to interpret BS 7671 using a mixture of terminology ... and further clearly says that additional protection must already be present in the circuit in which it is installed.
So, this isn't just BS 7671 we're discussing here, but the product standard itself.
Sparkingchip:
The house that Dave is asking about was presumably installed as EEBADS without any RCD protection in the consumer unit or fuse board at all, indeed it is still possible to install some circuits in homes without RCD protection, though not lighting circuits anymore as they require RCD protection as of this year.
In the GN it actually says:
13.2.1
The effect of applying main protective bonding is most noticeable in TT systems
Sparkingchip:
Maybe the saving grace is that bonding is more effective in reducing touch voltages in TT installations than in TN installations.
Andy Betteridge
AJJewsbury:
That is exactly the point I was making, you cannot connect a RCD to a circuit and installation that is not adequately earthed and bonded or else a fault elsewhere in the installation may raise the voltage of earthed equipment downstream of the RCD to dangerous levels, a RCD does not remove the requirements for basic and fault protection along with the requirement to mitigate touch voltages.
The point I was attempting to make was than even in a fully correctly earthed & bonded installation a fault elsewhere can raise the exposed-conductive-parts downstream of the RCD (as elsewhere) to dangerous levels - e.g. >115V for 5s in a TN system or 230V for 1s in a TT system - the 'mixed disconnection time problem' isn't just something for inadequately earthed/bonded installations to worry about.
There is some advantage in having all your RCDs close to the MET (with the minimum of parallel paths on the c.p.c.s) - in that faults on your circuit are covered by the rapid disconnection time of your RCD and faults on other circuits shouldn't raise the potential on your c.p.c. relative to the MET (where both your c.p.c. and main bonding are connected) - but BS 7671 doesn't clearly advocate that approach (although perhaps hints at it in section 701).
- Andy.