Two high-power appliances on a single 40A RCD

Former Community Member
Former Community Member
I have an electric shower installed on a 40A RCD, in a room adjacent to my kitchen. The shower is only used in an emergency - i.e. when our gas boiler is unable to provide hot water to our main bathroom. I would like to take a spur from this 40A connection to use for a new double oven, which is rated at 32A. Can anyone advise on a safe and legal way to do this, ensuring that only one of the two appliances can be connected at any one time?
  • Former Community Member
    0 Former Community Member

    Sparkingchip:

    Assuming a decent job was made installing the shower circuit the fabric of the building will have to be dismantled or flooring and the floor lifted anyway, unless it is accessible in a loft or runs up surface fixed, so hat sufficient cable can be accessed to install a junction box to divert the cable.

    Then the additional equipment installed and alterations carried out, before making good again.


    That is probably half the work of installing a completely new circuit and getting on for the same materials cost.


    The cost of the cable to run back to the consumer unit, a RCBO and the other bits and pieces is not significant and I really cannot imagine the labour cost would be in the region of £800 for pulling a cable through a house, for that amount of money you can certainly take time and care doing it.


    Andy Betteridge 




    Thanks for the info - and particularly the estimate of possible cost. Cost is, perhaps unsurprisingly, a significant issue. This is particularly true in the context of the purpose of the exercise, which is to install a £400 oven.

    As a comparison, what do you think I should expect to pay for an alternative solution using either an MCB changeover switch or shower priority unit?

  • Oh dear we are all becoming far too agitated. The Ib is not greater than In for this circuit is it, there is no intention to use both cooker and shower at the same time. I have pointed out that this is no different to any domestic final power circuit. The cable is protected fully against overload. Nothing bad is going to happen anyway, and the circuit is fine as far as BS7671 is concerned.


    Then we get to the bit where the moral attitudes of "I know best" come in. The MCB may wear out if the customer is careless etc. It may but would then fail to contact rather than weld up (as you should know). This criticism may be applied to any circuit breaker, presumably in your installations of those on ring or radial power circuits, or lighting with filament lamps. Then we get to the "we must prevent both being used at once even by accident". Why is this, everything is under control and the only outcome is a possible MCB trip, so what? Then I am attacked for "unprofessional" something or the other just because you have not quite understood what BS7671 says. I give examples and no one likes them. This circuit is designed to power either the shower or the cooker, not both! I do know BS7671 rather well, I teach electricians to pass the wee 18th test very successfully. I am however often surprised by the lack of knowledge of what it really says, rather than even looking up the correct answers. The regulations operate in the same way as UK law, the law saying what you cannot do rather than what you can, just like BS7671. It may give some hints of what you can do but these are in the appendixes at the back or in the notes to various regulations.


    I pointed out that changing a CPD to a different greater value is notifiable under part P, You are changing the circuit to a new one by definition, you have changed its design and rating. You ask what code this should be given, and I would say none, in that it is compliant with BS7671 as you have all found out by now, although it may not be something you have seen before. Saying that is dangerous or likely to fail in some way fails to understand its usage, and is not accurate or true as I have pointed out. Long term slight overloads are a risk for circuit designs but you need to understand exactly what that means, and the interpretation being given by me for this circuit explains what you need to examine. These are the circuit loss, thermal time constant, installation method and real terms loading etc. so not just a yes / no question. The slight overload is not 1% overcurrent, it is enough to cause significant extra cable heating, and needs to take account of the fusing factor, so perhaps 30 - 40% or more. The diversity on a circuit includes all loads, and the times they are likely to be operational, which were explained in the OP.


    I think that everything has been explained several times now by me, and useful comments from some others. Use this as a thinking exercise, it is useful because you have probably never considered this kind of thing before, and it is the process necessary to design a more complex installation.
  • Former Community Member
    0 Former Community Member


    https://www.theiet.org/career/professional-registration/

  • cfcman:

    Hi

    This is my first (and only) port of call. Got a little more feedback than I was banking on ?

    I'm not sure what sort of pictures you had in mind, but here's one of the switch for the shower circuit (the shower being in the adjoining room). The switch spends its days in the "off" position. None of the appliances in the picture live on the circuit controlled by this switch.
    477004fe30dd506dfbdf042d4c24310a-huge-20191129_wall-switch_annotated.jpg




    Thank you for the photograph. I feel obliged to make a couple of observations (with all due respect):


    (1) It is not a large property, so a shower for emergency use seems a little lacking in credibility;


    (2) There isn't a lot of room for a double oven. I also note what appears to be a stack of at least three microwaves. ?

  • Former Community Member
    0 Former Community Member

    But that is kind of the point, is it not?  


    Is that a deflection or a cloud (sic)?


    Again, what diversity can you apply to a shower?


    Regards


    BOD



  • Farmboy:

    And electrical work is not a profession - thereby making us professionals. We are a trade, that may try to carry out work in a professional way but that does not make us professionals in the sense of Dr's, lawyers, architects, engineers, etc, so no grandisement of the trade please.




    That's an interesting viewpoint and one which I admire. One might, however, argue that design work is engineering and, therefore, professional. 20 years ago, a chum of mine (whose house was one of the first on a small estate) asked various building tradesmen whether they considered that they were professional or not. IIRC, they associated professionalism with experience and expertise. That is probably the modern interpretation.


    Another interpretation would be that a professional puts the client's interests first, but that a tradesman will sell whatever he (or she) can.

  • If it were mine I maybe inclined to use a 4 pole contactor with 2 n/o and 2 n/c contacts and a switch to power the coil, like https://www.expertelectrical.co.uk/chint-nc1-contactors

  • perspicacious:
    The simple issue was an existing circuit. A shower circuit. It had already been installed, presumably fit for purpose. The Ib was assessed when it was installed diversity applied, that formed the type/rating of OCPD and the cable. So In>=Ib.


    What diversity can you apply to a shower?


    Regards


     BOD




     

    But that is kind of the point, is it not?  ?
  • Assuming a decent job was made installing the shower circuit the fabric of the building will have to be dismantled or flooring and the floor lifted anyway, unless it is accessible in a loft or runs up surface fixed, so hat sufficient cable can be accessed to install a junction box to divert the cable.

    Then the additional equipment installed and alterations carried out, before making good again.


    That is probably half the work of installing a completely new circuit and getting on for the same materials cost.


    The cost of the cable to run back to the consumer unit, a RCBO and the other bits and pieces is not significant and I really cannot imagine the labour cost would be in the region of £800 for pulling a cable through a house, for that amount of money you can certainly take time and care doing it.


    Andy Betteridge
  • Former Community Member
    0 Former Community Member

    weirdbeard:




    cfcman:

    I have an electric shower installed on a 40A RCD, in a room adjacent to my kitchen. The shower is only used in an emergency - i.e. when our gas boiler is unable to provide hot water to our main bathroom. I would like to take a spur from this 40A connection to use for a new double oven, which is rated at 32A. Can anyone advise on a safe and legal way to do this, ensuring that only one of the two appliances can be connected at any one time?




    hi cfcman out of interest, have you posted this query in any other forums or is this your first port of call? Any pictures you could provide might be really helpful in helping you with your query :)


     




    Hi

    This is my first (and only) port of call. Got a little more feedback than I was banking on ?

    I'm not sure what sort of pictures you had in mind, but here's one of the switch for the shower circuit (the shower being in the adjoining room). The switch spends its days in the "off" position. None of the appliances in the picture live on the circuit controlled by this switch.
    477004fe30dd506dfbdf042d4c24310a-huge-20191129_wall-switch_annotated.jpg