davezawadi:
What is wrong with simultaneous use, it will trip the MCB at some point, strangely that is what the MCB is for!!!! Belt and braces efforts at design are not required. Kitchen fitter does not have a clue! I wonder which regulation that is? Answers on a postcard to the Screwfix forum.
mapj1:
It is not illegal. It may be out of his comfort zone, which is fair enough, but then he should be honest about it. Be aware that wiring in bathroom zones (i.e within 60cm of the bath or shower cubicle ) requires notification under part P, and he may not be keen to get involved in that, or he may be worried that he gets called back if something trips.
If it was my house, and I know who will use it, I'd parallel them up and have a variation on the single line working token system for Victorian trains, - perhaps when the bar of soap is in the kitchen it is OK to cook, when someone takes it into the shower it isn't. Or a label on the shower for visitors - "check is anyone cooking ? Do not overload the trip !" Actually cooking is not as thirsty as folk often imagine - once initial heating is over the thermostat pings on and off and the average current is quite low. It is a cold start that is the problem.
Sparkingchip:
I have not disagreed with Zoomup ?