perspicacious:
What is wrong with simultaneous use, it will trip the MCB at some point, strangely that is what the MCB is for!!!! Belt and braces efforts at design are not required. Kitchen fitter does not have a clue! I wonder which regulation that is? Answers on a postcard to the Screwfix forum.
On carrying out an EICR and finding this, how would you code it everyone?
Regards
BOD
davezawadi:
Alcomax
See the post to Andy.
That Ib is potentially larger than In is not in itself a problem but perhaps slightly unusual. In this case I suspect that it is entirely satisfactory for the reasons in the OP. The regulations are all limitations to what you can do. This circuit is exactly the same as any other final circuit, it is subject to protection against overload for long periods. There is no regulation simply because it is not prohibited. Surely you have been taught that at some point. Perhaps this is the reason why electrical designers and installation assessors need to be somewhat skilled?
Can anyone advise on a safe and legal way to do this, ensuring that only one of the two appliances can be connected at any one time?
Which regulation says that you may not connect more loads than the CPD rating? Actually none as you well know from ring and radial final circuits.
Please list the regulation number you are citing immediately for the basis of your advice.
You are giving FALSE advice to a member of the public who has come to the IET for proper information. There is nothing wrong with his idea