Sparkingchip:
Back in the days when all loop testing was carried out at high currents before there were RCDs in the circuits and installation some specifications said that fuses had to be replaced after the loop testing had been completed, because the stress put on them by the loop testing could lead to early failure.
So at one time some fuses such as 5 amp fuses in lighting circuits were considered scrap after having 20 amps whacked across them got a very short period during a loop test.
Circuit protective devices are not indestructible.
Andy Betteridge
A short pulse of high current has very little heating effect anywhere, and is basically the adiabatic formula at low current and very short period. You can test this yourself again by calculation.