Hence the otherwise rather odd requirement to bond to the consumer's pipework (after the meter) rather than the service pipe before the meter
AJJewsbury:
Aren't all internal gas pipes required to be metal and not plastic?
Yes, but there can be insulating joints - sometimes specified at gas meters (internal or external) specifically to reduce the chances of currents flowing through the gas pipework. Hence the otherwise rather odd requirement to bond to the consumer's pipework (after the meter) rather than the service pipe before the meter.
- Andy.
To summarise, the two main reasons for insulating inserts/insulation joints in metallic pipework are to prevent corrosion and to prevent pipes being used as a path for fault current. Also, the main protective bonding requirements in BS 7671:2008+A3:2015 are understood to be written on the expectation that insulating inserts /insulation joints are installed in metallic service pipework.
It is important to be aware that this article only gives a brief overview of the issue of insulation inserts.
411.3.1.2 says, regarding main protective bonding, "IN EACH INSTALLATION"..... so we are not concerned with anything OUTSIDE the installation are we.
It's worse than odd.
It both defeats the purpose of the bonding rendering it useless and leaving the extraneous-conductive-part not bonded, and
the insulating section makes the consumer's pipework NOT an extraneous-conductive-part which therefore does not requiring bonding.
AJJewsbury:
411.3.1.2 says, regarding main protective bonding, "IN EACH INSTALLATION"..... so we are not concerned with anything OUTSIDE the installation are we.
But inside and outside the electrical installation isn't the same a inside and outside the building - as the electrical installation often extends outside (the building) these days.