Caravan electrical hook up?
I've been asked to install a supply to a hook up for a caravan in a garden.
I see that the connection of a PME earthing facility to any metal work is prohibited, is there anything else I may have overlooked?
Thanks in advance :)
  • Lyle, I don't disagree with what your last post, except that the "occasional hookup" is often not really that occasional - they are often left connected for extended periods, sometimes months.
    However, you will grasp from my post that I don't think we should be throwing in a separate TT earthing system ... particularly in small curtilage properties, I don't think it's an option - and neither is converting the whole property to TT on many residential streets and roads.
    Possibly a separate debate, but perhaps we should be moving towards open-PEN detection devices, developed for EV charging systems, as a better compromise in situations where caravans or mobile/transportable units are to be powered from premises in built-up areas with PME supplies? The ESQCR is perhaps a blocker, at least "officially" to a potentially safer approach for such hookups in dwellings.
  • What is the solution for an ordinary person with a newish house (TNC-S) having an outside socket probably connected to installation earth terminal rater than a separate rod and deciding to hook up their caravan in the drive to their household mains power. Do we warn them it could compromise safety or do we leave `em to it?
  • Ref. the back garden caravan. Would it not be better to supply it via a 1:1 isolating transformer if the loads are just lights and the occasional use of a computer or phone charger charger etc?
  • ebee:
    Just how conductive is drive block paving on sand or tarmac?
  • Current front drive caravan living.
    https://www.bbc.co.uk/news/uk-england-52280264
  • Zoomup:
    ebee:
    I would imagine that it could be quite conductive at times Zoom
  • ebee:
    Whilst Zoomup raised a good point, it's still technically in breach of ESQCR ... but I think it will be the DNO to whom the legislation applies ... tricky !
  • Some of my work involves high frequencies and short pulses, where it is quite possible for many reversals of voltage to exist in the 1m or so distance of a step voltage - if you like not only is there a voltage gradient between your feet, there is also a phase shift, of more than one rotation .My view and description on what an earth electrode is for is coloured by that view.
    I do not think we should talk about 'the' earth voltage as if there is some 'plate at the end of the universe' (apologies to fans of Douglas Adams)  at zero volts and we must connect to that by putting an electrode far far away. This is a  simplification that makes  text books easy to write.
    Rather I think there are many  things we can refer to as 'an earth', but these are not always at the same voltage as each other.
    What I think is more important for the shocked user  is the local voltage gradient - we need the car, caravan or boat to have  the smallest sensible  offset voltage relative to whatever else is in touching or stepping range.
    To me the most useful 'earth' is the potential of the terra-firma beneath your feet - but by that definition, your earth does not have to be at the same voltage as mine, and generally will not be.
    (Rather like the birds that perch on the 11kV line  - their local earth is approx 6kV RMS different from mine, but two birds on the same wire can come along side each other without incident, however if I being earthed to terra-firma were to touch the wire, or touch the birds for that matter, it would be very bad indeed for both of us - to the birds I am live and 'off earth' . To me however, their "earth" is what the RADAR  power supply folk and some particle accelerator texts call a "flying deck"  - they could, if they were not birds, build sensitive electronics things into little metal boxes and earth them to the wire and as far as the kit in the boxes was concerned no voltage gradient would exist. )
    Now Annex H4 is about car charging and correctly points out that a leaking PME service (or indeed anything injecting a voltage ) under ground creates voltage contours on the surface., and if you place the TT electrode in that region of influence, the voltage on the electrode  bounces up and down in time with the voltage on or near the surface.
    Thinking cars, but realizing metal framed caravans are similar (a wooden one would not matter so much )
    If you park your car such that is straddles such a fault, then it will couple to the surface like a parallel plate capacitor from the under body, and via the tyres resistively.
    Both of these are weak effects, at 50Hz capable of passing only tens of microamps for 230V.
    But if you stand beside the car, you too are at this local terra-firma surface  voltage and what you do not want to do is to earth the car body via a CPC to some potential widely at odds with your own.
    The PME earth voltage is obviously not the right thing, nor is a TT  electrode voltage from several metres away.  Ideally the electrode would be under the car, but  sensibly near is the best we can do.
  • mapj1:
    Mike,
    The gradient depends on the electrode arrangement, but in the case of one to three rods in line uniform soil, drops off over a relatively short distance of 2.5 m by a drop of about 70 % (See Table 16 in BS 7430).
    So yes it depends on where the electrode is, but if it's one side of the van, the influence of the electrode at the other side of the van is only 30 % of what it was ... but you can touch any metal frame earthed via the rod !
    This is important, if you just happen to be standing over any buried metalwork connected to the PME earthing system, and there's nothing connected to PME on the other side of the van to help equalize the rod potential with the PME system ...
    I think in this case Zoomup's comment regarding the high resistivity of driveway materials is probably more pertinent to shock risk reduction.
  • Is the ESQCR flawed by requiring that the NE link is at the supply cut-out?  Unless I'm much mistaken, in the USA, the link is in the consumer unit instead.
    Moving the NE link to the consumer's side allows something like a VOELCB or over-voltage trip to totally isolate the house from the incoming supply.  If we then require insulating sections in any supply pipes (gas, water, etc.) that aren't already plastic, then it should be possible to totally isolate the house from the supply in the event of a broken PEN.  I can't think of any likely situations where any other random extraneous conductive parts within the curtilage of the house are likely to end up connected to the public supply.