Au contraire the noo - See 314.1 (i).
Is there a requirement for MCBs to have reducing ratings working away from the RCD? ie, in reverse order: 40, 32 , 32......16,..6, 6 Or just common practice?
Jaymack:
On first opening this dual RCD unit, the 2 lighting circuits were on one R.C.D., and the 2 final ring circuits on the other R.C.D,, it was obvious also, that some wires to the new CB's were short and not lengthened, resulting in a bird's nest at the M.C.B.''s.
If you had a CU with two RCDs and four MCBs for upstairs ring main (32A), downstairs ring main (32A), kitchen ring main (32A), and outside socket (16A) then how would you connect them up, and why? If you then had to add circuits for a cooker (32A) and a central heating boiler (16A) which RCDs would you connect them to, and why?
AJJewsbury:
Is there a requirement for MCBs to have reducing ratings working away from the RCD? ie, in reverse order: 40, 32 , 32......16,..6, 6 Or just common practice?
Just good practice as far as I'm aware - if the larger currents involve only the shorter lengths of bus-bar then the overall heating is minimised. Pretty minimal effect in any event I would have thought.
- Andy.
mapj1:
I think this is the politicians use of the word "minimise" of the inconvenience, meaning 'not make it overly big' rather than the engineering one where we really mean 'make it as small as is possible'
AncientMariner:
davezawadi:
..... A quick swap around of a couple of MCB's would fix it anyway.
Is there a requirement for MCBs to have reducing ratings working away from the RCD? ie, in reverse order: 40, 32 , 32......16,..6, 6 Or just common practice?
Clive
AncientMariner:
Is there a requirement for MCBs to have reducing ratings working away from the RCD? ie, in reverse order: 40, 32 , 32......16,..6, 6 Or just common practice?