This discussion is locked.
Farm earthing arrangements.
Some years ago I started doing electrical work at a farm, originally the farm buildings and house were both connected to the DNO earth terminal.
I altered it so that the farm buildings are TT , but left the house connected to the DNO earth terminal. The possible issues are that there is a steel clad switch fuse enclosure for the house inside a wooden cupboard in the farm workshop and the SWA cable for the house passes through the ground immediately adjacent to the farm building. But there was no physical connection between the house and farm earthing arrangements.
It had been like that for a few years as the house has not had any alterations at all, just a few repairs. So the house installation is effectively exactly the same as it was when the house and the farm buildings were thirty years ago and connected up as a new installation by the DNO.
However (you knew there was going to be a however!) a couple of years ago PV panels were installed on the farm building roof and the installers used the DNO and house earth terminal rather than the farm buildings earth terminal, despite the PV system being in and on the farm buildings and it having storage batteries that feed back into the both installations as they share a meter; and the storage batteries act as a supply to emergency lighting in the farm buildings when the installation is off-grid.
I am now reviewing the earth arrangements, the house is empty and needs tidying up, thirty two lights need replacing and odd repairs, there won't be any alterations it is just replacing fittings and replacing MCBs in the split load consumer unit with RCBOs to give additional RCD protection in the house.
I will leave it at that and not express my thoughts, as it will be more interesting to see what your thoughts are rather than trying to get you to consider mine.
Comments please.
Andy B
  • Regular inspections of the overhead lines and equipment is carried out from a helicopter, so the yellow warning sign on the pole supporting the transformer and cables was replaced a while ago, presumably because it was not clearly visible from up in the air. Inspecting the earthing arrangement is obviously a bit more difficult.
  •   But I'd have thought there'd be occasional inspection (10yr?) to check the basics at LV transformers, e.g. soundness of main electrode, wire to it, pole, etc., which would be the opportunity to check that there's a record and that it fits the fact.  Do they have a chosen policy or obligation of checking through the system, or is it only a reactive service after complaint.
    I went for a walk today by the sea. I live in North Norfolk. There is a short section of bare overheads supplying a few properties on a cliff. Most overheads have been updated to A.B.C. insulated conductors in this area on the main roads. The wooden poles have aluminium plates on them with dates. I can see some dates punched out. It appears that ten year inspections are carried out. But the bare overhead conductors have lost their spacers, and in high winds are likely to blow about and short out as well. The last pole had an earthing conductor and earth rod, so presumably can be considered as P.M.E. The bare overheads are old and there appear to be many inline joints. The straining wire turnbuckle of the last pole is very rusty and may be weaker than is desirable.
  • Regards keeping records, I presume the WPD engineer dismantled the head as he did an earth loop test, I have not been to have a look but he said he wrote the loop test result and earthing arrangement type on the intake in felt pen for future reference, that's good record keeping.
  • Sparkingchip:
    Around here U.K.P.N. does it the posh way. The details of Ze are written on a white purpose made sticky label.