AJJewsbury:
Just as long as the FCU is capable of being secured if it can't be supervised by someone working on the boiler - most are these days - but not all were. Also capable of breaking N as well as L if it's a TT system.
- Andy.
OlympusMons:
so 510.3 if the MIs stipulate
132.15.201 if necessary to remove danger
And possibly, if it has an electric motor, 132.15.202