Hello All,
Scenario is; conversion of basement with a 3P supply to 3 separate flats. TNCS. To get a new CU into the furthest flat I've proposed 25mm singles in Scottish Power red conduit. The conduit would be run in the correct zone in a void about 100mm above a plasterboard ceiling with no insulation at this point. I get the max current to 80A for this method and a fused switch would be installed at the origin after the DNO cut out Have I missed anything here? I'd assume to measure volt drop to the origin and disconnection times to the CU as per.
Thanks for your time,
Pete