RichardCS2:
So, at a friend's house there is a 6 mm^2 bond to an up-and-over garage door, fitted so far as I can tell when the house was built in 1990. I would expect all the houses on this estate to have them though I haven't checked. Now would anyone like to argue that the risk associated with this large metallic surface with a conductive handle, touched regularly whilst standing on the driveway and connected to a PME-labelled earth terminal is significantly different to the car plugged in on the driveway?
Yes it could be argued that this connection could be removed, though on a wet and windy day perhaps the door measures just a few kiloohms to true earth and it is simultaneously touchable with a bonded metallic gas pipe. It may even make contact with the pipe some of the time, at the moment there's a ~1 mm gap but that could easily disappear.
I am unconvinced that there is a new risk associated with TNC-S and electric cars, rather that the risk is comparable to the others that have existed since the start of the PME era and have either been ignored, not been recognised at all, or deemed acceptably low.
gkenyon:
So, "back in the day" it might have been the right thing to do, to bond that garage door, but today (and for well over 25 years) it's perhaps not been thought of in the same way.
Chris Pearson:
There may well be many other instances of potentially dangerous outdoor metalwork (we have galvanised conduit which serves our outbuildings - incidentally, the supply was TN-S when it was installed) but that doesn't mean that we can ignore new ones.
RichardCS2:
More generally, the collision of risk approaches between the automotive and electrical worlds is interesting.
This is all explained in Annexes H and I of the 4th Edition of the EV CoP. Very briefly