gkenyon:Sparkingchip:
I cannot think of any installation dead tests that cross wired installation would not pass.
Andy BSo a Ze or ZDB test could check for a supply wiring error? I think that's back to where we were - discussing live Zs tests on ALL final circuits.
You have to do a live test somewhere along the line.
Three phase you will be checking the phase sequence as well as polarity, I had an interesting discussion with two electricians in a pub one night, one of them works for a generator hire company and makes great use of a long wander lead to ensure he is hooking up temporary supplies correctly.
Andy B.
lyledunn:Sparkingchip:
I cannot think of any installation dead tests that cross wired installation would not pass.
Andy BIndeed Andy. It looks like the tester you are using is of the type that would alert you to a live line conductor even if another potential was not available. Some testers do not offer that facility and one needs to be careful as say a polarity reversal on a TNCS system would not be apparent when tested at a single-phase intake.
It self tests as well.
Andy B.
Sparkingchip:
I cannot think of any installation dead tests that cross wired installation would not pass.
Andy B
Indeed Andy. It looks like the tester you are using is of the type that would alert you to a live line conductor even if another potential was not available. Some testers do not offer that facility and one needs to be careful as say a polarity reversal on a TNCS system would not be apparent when tested at a single-phase intake.
Sparkingchip:Chris Pearson:
I'll bet you any money that those RCBOs are not tested monthly!The single pole RCBOs are all in the off position, remember the bit about single pole devices having to be in the live conductor, that's not much use when there is reverse polarity on the entire installation.
OK, so the tenant diligently presses the test buttons and nothing happens; but the lights come on, the telly works, heaters get hot, and motors go round and round. Does he (or she):
(a) notice?
(b) think that it is a bit odd, but they are all the same?
(c) ask a question in here?
(d) panic?
(e) isolate and request an emergency call out from the nearest qualified sparks?
Chris Pearson:
I'll bet you any money that those RCBOs are not tested monthly!
The single pole RCBOs are all in the off position, remember the bit about single pole devices having to be in the live conductor, that's not much use when there is reverse polarity on the entire installation.
Andy B.