RustyH:
Just so I understand, why does a 13A FCU Spurred from a ring and feeding a 1.9Kw device that would probably be deemed as fixed would be totally inappropriate?
As mentioned in the previous posts, there is the motor inrush to think about so not to cause nuisance tripping, but as the client has been running this on a 13A plug with no blowing of fuses up tripping, the inrush must be below a current, or for a short enough time that doesnt blow / trip fuses.
Then there is the MIs, thanks to Olympus for finding them. I believe from the points in the MIs, the only one that would deviate is the american term of a dedicated branch (I.E: its own dedicated feed).
However, the above spur idea would meet the required circuit protection
The Mis mention "DQG have a leakage current that may exceed 10mA", I have no idea what a DQG is, but over 10mA and 543.7 comes into play. And other devices on the ring will add to the leakage.
The 75degC requirement means a higher temperature rated cable might be needed, at least for the connection. It is the only requirement in capital letters.
They also say a dedicated circuit. Ring circuits can be prone to discontinuous conductors, I have had a rodent problem, I know.
Can't think of any more at the moment.