The only way to do this is very bureaucratic and would be a "Technical construction file" or TCF
davezawadi (David Stone):
. . .On another note my playing with RCDs is still proving interesting, and I am not at all convinced that an RCD with a high fixed load still trips at 30mA or whatever, particularly if the waveform is not ideal. Perhaps there is more to this than meets the eye.
My understanding is that once you are over the rated current of an RCD by a certain amount, you may magnetically saturate the sensing coil, leading to either no operation or operation at a higher than desired current.
Regards,
Alan.
Alan Capon:davezawadi (David Stone):
. . .On another note my playing with RCDs is still proving interesting, and I am not at all convinced that an RCD with a high fixed load still trips at 30mA or whatever, particularly if the waveform is not ideal. Perhaps there is more to this than meets the eye.My understanding is that once you are over the rated current of an RCD by a certain amount, you may magnetically saturate the sensing coil, leading to either no operation or operation at a higher than desired current.
Regards,
Alan.
Not quite that bad if it is working properly - the current the core sees is the difference of the two fields that would be created by the L and N windings. Ideally these cancel when L and N currents are equal and opposite.
In reality, winding geometry variations and core material tolerances, conspire to mean cancellation is jolly good but not perfect, typically parts in 10 000 or so.
As far as the sensing and tripping circuit goes his gives the equivalent of a standing AC leakage that is equivalent to a small fraction of the load current - if it was 100A load , and 1 part in 10^4, imbalance then this would look like a 10mA leakage, even on a perfect load, before the real leakage kicked in. This may be in our out of phase with any real leakage, so when a fault comes on the device may appear more or less sensitive than it did for a very low load. However, it can never be more deaf than twice the trip threshold, as that is the worst case, when the internal imbalance is almost tripping the device, and in perfect antiphase to the fault current. Equally, if the load and the internal imbalance terms were in phase it could make the unit hair-trigger sensitive wnen fully loaded.
Sometimes this effect is blamed when RCDs trip on switch on for large loads, but this can also be due to real out of balance current flowing that are higher than the steady state value while mains filters with capacitance to earth stabilize.