the earth resistance at the farm needs to be very low and the earth resistance of the transformer electrode a lot higher in proportion to get a 187V rise
John Peckham:
In your diagram the earth resistance at the farm needs to be very low and the earth resistance of the transformer electrode a lot higher in proportion to get a 187V rise and that assumes any PME electrodes are not there or also very high resistance.
Who said anything about PME? It could well be a TN-C-S version of PNB, or anything else which the DNO fancies. If there are multiple earths, why are they not pulling down the local ground potential?
lyledunn:
Above is my interpretation. There are no common services.
OK, thank you, that's interesting. The tap can only be at 0 V if it is bonded; but if the water supply is metal, why has it not reduced the ground potential by the tap? Or is it a plastic supply, and if so does this illustrate that under a rather unusual set of circumstances, unnecessary bonding may be hazardous?