Supply for a camper van.

A neighbour has just bought a camper van and I noticed that it is plugged into a garage socket whilst it is on the drive. I guess this so that they can do any fitting out it needs and keeping it's battery charged.


Having been reading the posts on EV charging, I am wondering whether similar requirements would apply to a regular 13A socket whether inside the garage, or outside the garage?  The supply is 1-phase TN-S 

Clive
  • To clarify, the supply in question is TN-S and not PME/TNCS with the lead sheath of the PILC cable.


    Both houses built circa 1957. As I have previously posted, when we had our meter moved in 2002, I was offered PME/TNCS on the day if I wished for it instead of the TN-S as it was with the PILC cable into the cutout. (They used split-con and I watched the DNO's Jointer sweat the 5 un-insulated copper earth conductors onto the lead sheath.)


    Going back to the early 1970s when we were house hunting, I noticed at a recently built house in Chester. there was a P.M.E. warning label on either the cut-out or adjacent to it on MANWEBs board. The house we eventually bought in 1973, in Wales but still within MANWEB's area, was TN-S. Again split-con from the cut-out next door which was supplied by a PILC cable.


    Surely if a DNO is changing the earthing method, at the very least they should notify the house holder, even if the householder does not understand the technicalities?

    Clive
  • I does seem reasonable Clive but I`m afraid not. The just Joint the N & E then bring it to the cutout as TNC-S with adjoining properties not far away they also effectively have a pretty much TNC-Sish supply too
  • ebee:

    I does seem reasonable Clive but I`m afraid not. The just Joint the N & E then bring it to the cutout as TNC-S with adjoining properties not far away they also effectively have a pretty much TNC-Sish supply too


    That was exactly my experience. When my service cable was "PME'd" under the lawn, I asked why they would not repair the poor joint. I was told that all the lamp posts are "PME'd" anyway so it wouldn't make any difference. I assume that meant that there were N-E bonds at each one +/- some form of earth connexion. So if you don't know, you'd say TN-S 'cos that's what it looks like.


  • UKPN:

    Any infringement of the ESQCR regs will be dealt with firmly and swiftly by the DNOs. As was witnessed when the picture guide book came up with the hairbrained scheme to "improve" the DNOs network. This was the horror whereby many rods were to be installed in peoples front gardens and patios to "reduce" an already low impedance. Ill conceived, needless to say didnt get past the sham "public" consultation period. 


    Clash head on? I think our poster is flattering himself, there will be no clash, if incidents are reported to the DNO regarding  a PME breach the consumer will be at risk of losing the facility on safety grounds. (By law)


    "its the supplier who has the duty to comply" Not true, It is the designer/specifier/installer who must be clear of their of their reasons and acknowledge their accountability in making such a decision.


    Regards UKPN. 


     


    If you have a look at the specific Regulation 9 of the ESQCR, it's clearly a duty of the Distributor ...


    Nothing in the Regulations serves to impose a duty on the consumer in this respect.


    Whilst Regulation 26 may permit the DNO to disconnect, in this case there's not a problem with the  consumer's installation, as it's only what's plugged into a socket-outlet that arguably causes a potential safety problem.


    ... which is probably why 1000's of caravans and motor homes are plugged into PME installations at homes around the country, and nothing is done about it ...


  • davezawadi (David Stone):

    Surely a motor home is a motorised caravan, so is subject to section 717, and the parking space section 707. The dangers are exactly the same as electric vehicle charging, and a shock between the vehicle and the ground around it, or PME earthed extraneous parts close by, is equally possible. I have not noticed many owners taking any notice of these regulations in my locality, either with motor homes or caravans.


    From BS 7671 perspective, it's effectively a caravan.


    But I agree ... in reality, I don't think there's a difference with an electric vehicle - if anything perhaps less of a risk because it's only 16 A not 32 A or more.


  • davezawadi (David Stone):

    Surely a motor home is a motorised caravan, so is subject to section 717, and the parking space section 707. The dangers are exactly the same as electric vehicle charging, and a shock between the vehicle and the ground around it, or PME earthed extraneous parts close by, is equally possible. I have not noticed many owners taking any notice of these regulations in my locality, either with motor homes or caravans.


    That's because the average householder doesn't even know those sections exist.  There's no requirement for a householder to comply with any particular British Standard when putting a 13A plug into a 13A socket.


    That's the daft thing about it all.  We have the ESQCR and BS7671, and all their ridiculously complicated rules.  But the average householder knows nothing about them.


  • Simon Barker:
    davezawadi (David Stone):

    Surely a motor home is a motorised caravan, so is subject to section 717, and the parking space section 707. The dangers are exactly the same as electric vehicle charging, and a shock between the vehicle and the ground around it, or PME earthed extraneous parts close by, is equally possible. I have not noticed many owners taking any notice of these regulations in my locality, either with motor homes or caravans.


    That's because the average householder doesn't even know those sections exist.  There's no requirement for a householder to comply with any particular British Standard when putting a 13A plug into a 13A socket.


    That's the daft thing about it all.  We have the ESQCR and BS7671, and all their ridiculously complicated rules.  But the average householder knows nothing about them.




    The legislation in this particular case influences the intendant "British Standard Requirements" ... and so the circle keeps being "squared".


  • Simon Barker:

    That's because the average householder doesn't even know those sections exist.  There's no requirement for a householder to comply with any particular British Standard when putting a 13A plug into a 13A socket.



    That's the daft thing about it all.  We have the ESQCR and BS7671, and all their ridiculously complicated rules.  But the average householder knows nothing about them.




    Quite so. Why would an ordinary person think that there were any restrictions as to what may be plugged into a 13 A socket? It isn't obvious that an EV shouldn't be plugged in via an extension lead even if it goes across the road. Nor for that matter is there any reason why an ordinary person would know that the total load in a double socket should not exceed 13 A.


  • in reality, I don't think there's a difference with an electric vehicle - if anything perhaps less of a risk because it's only 16 A not 32 A or more

    Indeed. As technology is moving on there less of a difference between caravans, EVs (and as davezawadi mentioned) mobile & transportble units - yet BS 7617 currently has somewhat differing requirements for each - some of which would be incompatible with the ESQCR in some situations (charging a motorhome from PME earthed system). I hope that no-one thinks it a good idea that the new PME CNE break detecting and c.p.c. switching charge points should come with a label that says "not suitable for use with electric motorhomes".


    I'll have to see if the DPC offers any improvement, but perhaps now would be a good time to start thinking about lobbying for a change to the ESQCR to allow PME earth to be used for caravans where TT isn't suitable and suitable precautions are taken to automatically disconnect the vehicle (and charge point if it itself has exposed-conductive-parts) from the PME system (including PE) when a broken CNE is detected.


    I still reckon it would be logical to build that protection into smart meters.


       - Andy.
  • Have a look at 717.411.4.