In more recent cabling, the three live phases are all insulated in brown (with neutral in black and the earth green and yellow). So now it is nearly impossible to identify which phase goes into which house.
davezawadi (David Stone):
That Andy is complete rubbish. You say you carry out EICRs, well I think you shouldn't for obvious reasons. You simply do NOT understand the regulations! BS7671 is not saying that domestic installs must use a CU (they can use any switchgear they require). In a large house with perhaps 20 bedrooms and commercial sized kitchen, electric heating, etc, you would expect to install a CU although you have a 3 phase 200A head? You simply have a completely wrong idea here. Why can you not fit a CU? I expect you will have some difficulty finding out, despite having the CU standard in front of you!
It clearly says “shall comply” and “and shall”.
Where is it proposing an alternative?
Andy Betteridge
Sparkingchip:
Is there such a thing as a BS EN 61439-3 compliant three phase domestic consumer unit?
Common 3ph DBs would still meet that spec.
For example, Schneider Isobar type B:
https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=Cat_FD.pdf&p_Doc_Ref=Cat_FD19UK
(Page 27 references BS EN 61439-3)
I would note that BS EN 60439-3 was superseded by BS EN 61439-3 in 2012. So you won't find any new CUs of any size claiming it (one hopes), which might be impeding your search?
tattyinengland:
Surely a three phase distribution board is always made of metal? I've fitted a few three phase domestic DBs over the years and dont kn ow why they wouldn't comply? I certainly wouldn't call them "domestic" though as they are the same DBs I'd fit in a commercial building.
I didn't know you could get a three phase DB any other way unless you used three single phase boards perhaps? These would then be metal anyway?
Kind Regards
Tatty
I met a plastic 3ph DB fitted by an overseas contractor working in the UK. It was in a HV switchroom so got removed sharpish as it didn't meet spec in all sorts of ways. But they exist.
when drafting a legal document, the term shall is used to say that something must be done, as opposed to the term may which simply means that something is allowed (ie that it can be done, but does not have to be done)
https://www.translegal.com/dictionary/en/shall/verb
Jam:Sparkingchip:
Is there such a thing as a BS EN 61439-3 compliant three phase domestic consumer unit?
Common 3ph DBs would still meet that spec.
For example, Schneider Isobar type B:
https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=Cat_FD.pdf&p_Doc_Ref=Cat_FD19UK
(Page 27 references BS EN 61439-3)
I would note that BS EN 60439-3 was superseded by BS EN 61439-3 in 2012. So you won't find any new CUs of any size claiming it (one hopes), which might be impeding your search?
There is a reference on Page 51.