Ian Hildrew:
Nowadays to reduce the susceptibility to nuisance tripping, good electricians fit every circuit with its own RCBO. Not the cheapest option but it saves call outs from customers. In these cases there is no need for another upstream RCD unless the setup was with the S curve 100mA RCD situated remotely from the CU.
Yes but the RCBOs would need to be double pole to avoid the S type coming out on a neutral earth fault after the final circuit RCBO had tripped.
ebee:Sparkingchip:
Why did councils specify 100 mA main switches in consumer units with TNCS earthing back in the late 1970’s, rather than a 30 mA?
Not a trick question, I do not know why.I have not come across that one Andy, could it be a regional thing
I have found them all over the country, one sticks in my mind, I drove from Worcester to Morecambe to do a job knowing that the survey photos showed a RCD main switch and when I got there it was a 100 mA.
Mind you quite often I get sent photos of the CU with the cover closed, so as to retain life’s little mysteries.
UKPN:
As our poster knows, I am talking about an all steel box, but let's not let the facts get in the way of a good topic.
Regards, UKPN
The point I'm trying to make is that a steel box does not necessarily mean that something is entirely class I - in the case of steel consumer units some manufacturers provide 'insulation kits' that provide double/reinforced insulation to the incoming tails - thus removing the need for an external upstream RCD where there is an RCD incomer or the internal construction is double double/reinforced insulation up to the RCBOs etc.
Personally I'm not entirely convinced by some of those kits, and so would prefer an upstream RCD in its own insulating enclosure - but I can only claim that as a personal preference, not a legal requirement.
- Andy.
a glorified grommet
AJJewsbury:
(As I mentioned before, personally I don't like that approach. The consequences of a L-PE fault before the first RCD is particularly nasty - imposing a hazardous voltage on the entire installation for a long duration........
- Andy.
And perhaps someone else’s installation!