TT installs are a rather special case, and only require a single fault to be dangerous
Nathaniel:
However, note that it's not just devices with a single-diode rectifier that could give a half-wave rectified residual current. A bridge rectifier can do this too, from either of its dc outputs. So half-wave rectified residual currents can arise from the wires and components that come after a rectifier inside an appliance, if these touch the frame or if a person directly contacts such parts.
This begs the question, "What is additional protection for?"
The obvious answer is to protect from direct contact when you have just mown or trimmed a power lead in the garden.
If there is a fault of negligible impedance just downstream of a rectifier, which is close to the supply of a piece of equipment, wouldn't ADS operate?
However, even if the fault is of negligible impedance, the circuitry between it and the supply terminals may have a resistance of several ohms so that even a BS 1362 fuse does not blow. Presumably, however, the touch voltage would be < 50 V.
Then I thought about a fault and circuitry which together have an impedance of say 8 kΩ so now we have a fault current of 29 mA and off she trips. So now I wonder whether some nuisance tripping of electronic devices is in fact due to a fault somewhere in the circuitry.
Is additional protection designed to protect us from relatively high impedance faults in equipment, or is it just fortuitous?