mapj1:
Indeed and modern earthed concentric and waveform cables are very like a low impedance coax, at least at these frequencies, and voltages between L-N or L-L tend to get smoothed out by that - indeed long range powerline comms, which I do not like for other reasons, relies on this transmission line bahaviour.
If you look at the design of nuclear bunkers, or EMP proof test chambers. you will see we very carefully try to bring all the services in through one "access panel", or at least one all-metallic wall, so that there is in effect an low impedance bond between comms lines and mains lines,, plumbing and similar. In the 'dipole' view of the world, while we cannot stop voltages being induced external to the facility but we can give the current an easy path that does not involve passing any significant fraction of it though sensitive equipment.
While this is not possible in most buildings, but it is worth bearing in mind as the only reliable way to protect equipment - so for example TV antenna feeders that are connected to the mains ground are less likely to blow up the TV they are attached to and soon .
Mike
Definitely, this is an approach that can help ... although it sometimes just "moves the problem on elsewhere". I've used it myself.
davezawadi (David Stone):
I don't understand that comment at all Graham. The induction into supply cables is close to completely common mode,
That would be great, but we ground stuff in a three-phase system. If we grounded single-phase at half the supply voltage, we would have far less of a problem, but that's not the case.
davezawadi (David Stone):
That is the point Graham. You are assuming that because one conductor of a transmission line is "Grounded" the rules of induction change. This is not correct, the same current is induced into both conductors, whether one or the other is connected at some point to some other thing, even the Earth. There are other phenomena that happen at the point where the line becomes less balanced or the connection to Earth, such as signal reflection which is asymmetric, but at the cable lengths we are discussing at a very low frequency, the effects are unlikely to be huge voltages particularly as the field strength is not very high.
Mikes point is also very important, induction into a screened cable (SWA, Wavecon, PILC etc) , is greatly reduced by the screening efficiency of the covering, although it may be induced into the screen material. This is a potential problem with PME, where N & Earth potentials at the intake could be some way above Ground without a ground connection, thus the reference to foundation Earthing I made above.
Low frequency is interesting ... the leading edge of impulses has a lot of HF components?
No point repeating here, though, what can be found on the subject of switching surges and impulses due to remote and local phenomena - and of course reflections on transmission lines.
In any case, I offer no "assumptions". It's difficult in a Forum like this to argue with "pseudo-science" in a forum like this - I guess what would be interesting is to see your views mapped against the relevant Clauses in BS EN 62305-4 and BS IEC 61000-5-2.
whjohnson:
So, might an accurate summary be that AFDDs offer nothing by the way of enhanced electrical safety for the domestic consumer, and that the merits of SPDs in a domestic environment are at best very dubious, and at worst, mere profiteering?
I'm sitting on the fence with regards AFDDs.
My experience tells me that SPDs in a domestic environment are far from profiteering, and are becoming / have become necessary in many homes. This necessity will increase as we move towards more smart controls etc.
I understand the point of view "why don't electronic product manufacturers build protection in" - well, why should consumers pay for a large number of electronic components to do the job of a small number in the electrical installation? At the end of the day, though, product standard govern what is in products, and if we want to complain at that, we should comment on those standards when they come up for DPC?
I guess when insurance companies stop paying out, or electricians have got fed up of replacing electronic products under warranty, opinions will change?