mapj1:
You may find that attaching the cable to a wooden 'heat spreader' means that side is better cooled - wood is not a good thermal conductor, but it is more conductive than the average block of celotex or what have you. A 3 or 4 inch dive in celotex would not worry me on 2.5mm cable or larger. By the time we are much thicker on the insulation I might be derating or slipping a metal plate or metal capping in there to diffuse the heat out a bit.
How the hell is a sparks supposed to know the U value of any insulation? (Methods 100 - 103, table 4A2.)
Tom, my apologies, I hijacked the thread a bit. ? Cables are found in masonry all over the place - domestics, the smarter common areas, the public side of hotels, etc.) and I have no doubt that "C" is correct and I agree with your rule of thumb.
In the example that I described, I went for 100# to be on the safe side. I don't know what was stuffed in the ceilings after I left. The only potential bugbear would be that 4 mm² would no longer do for a radial on a 32 A breaker.
I also agree concerning EIC as opposed to EICR - difficult to know exactly what is below (or above) the surface. Of course when you come to do an EICR, you will be presented with a folder containing the EIC and any previous EICRs will you not? ?
Presented with an EIC, thats happened nearly as often as i've won the Euromillions jackpot ?
The new fangled 100# are at least straightforward looking but only mention stud walls and ceilings. Pretty sure they'd all be "A" in old money.