Do not fancy 133 volts to earth on the shell of an E27 lamp
Sparkingchip:
Not something I am experienced with and I am never likely to be.
I did do a quick bit of reading last night and that left me wondering what actually happens under first fault condition such as touching a single exposed conductor?
In principle, nothing different to when touching a single exposed conductor on a UK type 230/400 volt system. Except at a lower voltage.
An electric shock at 133 volts would be received, less risky than at 230 volts but by no means benign.
The usual precautions should be taken to avoid contact with live conductors.
A suitable RCD would greatly reduce the risk of this shock being fatal.
For a 2 wire circuit, a standard UK type TRUE TWO POLE RCD would be suitable.
For a 3 wire circuit a special RCD intended for the lower voltage would be needed. These are readily available in countries that use 127/220 volt systems, the very similar 133/230 volts about which we are talking.
Do I use 0.8 seconds instead of 0.4 for my disconnection time?
AJJewsbury:Do I use 0.8 seconds instead of 0.4 for my disconnection time?
Table 41.1 puts the Uo boundary between 0.4s and 0.8s at 120V nominal - so as your Uo is 133V nominal (and TN), then by the book you should still be using 0.4s disconnection time for small final circuits (or 5s for socket circuits over 63A or other final circuits over 32A or any rating of distribution circuits).
- Andy.
I never understood that considering voltage at the fault point to remote earth will be lower.