It is a 5.2E unit so no earth fault protection and the faulty lift is still isolated. I can reset the device with no load, then as I start turning on the isolators to the 13 flats it trips after I get 5 or 6 on, any 5 or 6 so not a fault in one of them just when there's enough load, which was less than 20A across all the phases according to my clamp meter.
I can not read and digest all of the maker's instructions, but I wonder if the unit has defaulted into some kind of protective mode to prevent being reconnected onto a fault? It may not be faulty at all. I would contact the maker's technical dept. and ask them. The unit is very complicated and the maker's are the ones to diagnose the problem. It is just a matter of grasping the nettle and making progress here.