AJJewsbury:
Arguably if it's an existing circuit and you're simply replacing the appliance like-for-like, there's no requirement to bring the existing circuit up-to-date. Most would probably recommend taking the opportunity to do so - and the manufacturer's instructions for the new unit would most likely ask for 30mA RCD protection - but there might be a modicum of wiggle room there.
Is this DIY or paid work?
If DIY, there is no obligation to comply with BS 7671, nor is a like-for-like replacement notifiable.
If paid work, the circuit really ought to be compliant and, of course, a MEIWC will be issued.
Nothing has been said whether the premises are owner-occupied, vacant, or let.
I am confused because the regs seem to contradict themselves.
ebee:
Note ALL of the requirements will allow you to omit supp bonding. All not just any. Therefore main bonding must be in place if required and it must be continous from any metal pipework to any metal pipework in the bathroom, plus all ccts of the bathroom must be 30mA (or less) RCD protected and that includes all ccts running thru the bathroom as well.
Just to clarify that I do understand that all of the requirements need to be complied with, I was just trying to reduce the length of my post by omitting some text.
I think I am leaning towards biting the bullet and replacing the consumer unit, although I am going to take a look at the rest of the house before committing to anything. I have horrible feeling I am going to find multiple other issues and the project will snowball.