531.3.1.202

"It is not permissible  to introduce an external connection for the purpose of intentionally creating a residual current to trip an RCD."


What problems, hazard or danger will ignoring this regulation create?


Z.
  • Former Community Member
    0 Former Community Member
    If the RCD doesn't trip, what situation are you left with Z?


    Regards


    BOD
  • I`m not admitting that it was me but a "Noise Reduction Plug" a k a a resistor betwixt L & E in a plugtop to cut power to teenagers rowdy party whilst parent in bed , prove quite effective a few years back
  • Such a current would be applied downstream of the RCD. If the RCD trips, or is used as a point of isolation, and the arrangement tries to apply current, you are left with a current which might have nowhere to go except the person to whom additional protection is being offered, or whom the isolation was intended to protect.
  • ebee:

    I`m not admitting that it was me but a "Noise Reduction Plug" a k a a resistor betwixt L & E in a plugtop to cut power to teenagers rowdy party whilst parent in bed , prove quite effective a few years back


    That's not really an external connection, but it is intentionally introducing a residual fault current.


  • gkenyon:
    ebee:

    I`m not admitting that it was me but a "Noise Reduction Plug" a k a a resistor betwixt L & E in a plugtop to cut power to teenagers rowdy party whilst parent in bed , prove quite effective a few years back


    That's not really an external connection, but it is intentionally introducing a residual fault current.




    Where does that place the use of RCD testing?

    Legh

    Note 2.....531.3..1.201


  • Former Community Member
    0 Former Community Member
    That's not really an external connection, but it is intentionally introducing a residual fault current


    I think the Reg is worded so as to "discourage" the use of such a method for something akin to an "emergency stop button".


    Regards


    BOD (15th Qualified!)
  • If memory serves at about the time that reg came into being there were devies about that purported to detect a fire/overheating in electrical accessories and in such an event close contacts between L and PE via a resistor in order to trip the supply RCD. Needless to say there were a number of scenarios which turned a minor failure into variously dangerous situations, often compounded if the user reset the RCD without fixing the original fault.


    I might be adding 2 and 2 to get 5 of course...

        - Andy.
  • Legh Richardson:
    gkenyon:
    ebee:

    I`m not admitting that it was me but a "Noise Reduction Plug" a k a a resistor betwixt L & E in a plugtop to cut power to teenagers rowdy party whilst parent in bed , prove quite effective a few years back


    That's not really an external connection, but it is intentionally introducing a residual fault current.




    Where does that place the use of RCD testing?

    Legh

    Note 2.....531.3..1.201




    Or loop impedance / pfc testing for that matter ... it leaves those in the hands of electrically skilled persons, to be carried out using test instruments to a suitable [specified series of] standards that apply test conditions for limited times etc., and to be carried out only once basic safety tests have been undertaken.


    If carried out without some of the safeguards in BS EN 61557 series, the "upstream/downstream" method could inadvertently connect an upstream live conductor to downstream conductors that are supposed to be disconnected by the RCD for prolonged periods. And similarly, if carrying out the test to the associated protective conductor, currents in excess of those that can lead to serious electric shock effects might be applied for too long if an instrument to BS EN 61557 series is not used. Hence the inclusion of Note 2 (Part 6 calls out BS EN 61557).


    The RCD test button itself operates in this way, albeit through a high value resistor, which is why I guess the term "external connection" is used.  Interestingly, some RCDs have a disconnector contact for the test switch too, some don't - the current version of BS EN 61008-1, Clause 8.11, states "It shall not be possible to energize the circuit on the load side by operating the test device when the RCCB is in the open position and connected as in normal use." but it is not specified whether the in-built mechanism for achieving this is electrical or mechanical (or indeed a control interlock).


  • perspicacious:

    If the RCD doesn't trip, what situation are you left with Z?


    Regards


    BOD


    Proof that the R.C.D. is faulty, and .........................I suppose that it would be much like being in contact with the metal cap of a live neon mains' tester screwdriver. What happens if the  R.C.D.s test button fails to trip the R.C.D. off?


    Z.


  • gkenyon:

    Such a current would be applied downstream of the RCD. If the RCD trips, or is used as a point of isolation, and the arrangement tries to apply current, you are left with a current which might have nowhere to go except the person to whom additional protection is being offered, or whom the isolation was intended to protect.


    Yeh but it is such a tiny current originated through a big, erm, high value resistor.


    Z.