It seems there is no definitive answer and either a MCB fused Isolator or a cartridge fused isolator can be used providing they are double poled.
With regards to the RCD, if we were to put an additional RCD in the shed this would be just protecting the swa cable going from the shed to the consumer unit in the home.
Recently the DNO's have been replacing the old meters with new smart meters and a double pole isolator switch (in the meter box). They have not mentioned the lack of an RCD in the shed but have left a label saying the tails are undersized. The tails are currently all 10mm and they are requesting that they be changed to 25mm. This leads me to a a second question, as they seem to be replacing their existing cartridge fuses which were 60 amp with cartridge fuses that are 100a. My second question is what size tails are appropriate giving that our side of the meter we were only going to supply a 60 amp fuse max or a 40 amp fuse. I understood that for 10mm swa cable you should have no more then a 60 amp fuse. For this reason wouldn't 10mm tails or 16mm tails be sufficient? Also who is responsible for changing these if the connection to the isolator switch should be done by ourselves but the connection to the meter should be done by the DNO. Do I need to arrange this when both my electrician and the dno's electrician are there together?