Earth Leakage Current – How much is too much?
Hi All, I’ve recently started out and have my first customer with an intermittently tripping RCD and relatively high earth leakage current.  I’d appreciate some opinions on my diagnosis and thoughts on a solution that will guarantee to fix the problem and also be cost-effective.   Here are the details…
Installation:
Domestic, overhead PME supply
Consumer unit configuration:
80A Main Switch/30mA RCD combined (MK 7880s) feeding 11 MCBs i.e a single 30mA RCD protects all 11 circuits, date fitted estimate 1990.
Fault Symptoms:
(1) RCD Main Switch trips intermittently, randomly (i.e not coincident with equipment or appliances switching on/off, often when no-one is home), infrequently but frequently enough to be a real nuisance as it disconnects the whole installation.  On average the trip occurs once every two weeks, but a month could go by with no trips then, for example, it may trip three times in a weekend.  Tripping has occurred in all weather conditions but more often in stormy weather.  This has been happening since the customer moved in six years ago.
(2) RCD trips very occasionally when garage lights (5x fluorescent tubes) or tumble drier are turned on – this is much less frequent than the random tripping described in (1).
Investigation:
Earthing Conductor and Main Equipotential Bonding all present and correct.
All circuits have Zs within spec, measured at far ends of circuits.  Insulation resistance test of the whole installation (L & N to E at 250V) gives 37kohms.
There are no obviously faulty accessories or equipment and the installation is generally in good condition.
The RCD operation seems to be good; with all circuits disconnected it passes the no-trip test at 0.5I-delta-n and the disconnect times are 15.6ms and 11.1ms at I-delta-n and 5I-delta-n respectively; ramp test shows that the RCD trips at 23mA.
Earth leakage current (measured with an earth leakage clamp meter around the tails) with all MCBs closed and the installation “as found” (i.e nothing explicitly turned on or off) is 17mA.  A repaired ring circuit in the kitchen draws 6mA of the earth leakage, a garage circuit draws 3.3mA and the remainder is divided roughly equally between the other nine circuits (0.5 – 1.5mA each).
My Diagnosis:
The installation is not unsafe.
The RCD is (quite severely) sensitised by the 17.0mA standing earth leakage current, it will trip when a further 6mA of leakage current is drawn.
The fluorescent lights and tumble drier are likely to draw a transient earth leakage current >6mA when they start which explains symptom (2).
The random tripping, symptom (1), is being caused by supply side transients (or maybe even an intermittent fault in the overhead cable) and/or a high impedance neutral-to-earth fault somewhere in the installation.
Question 1:
What is the maximum level of earth leakage acceptable in any given circuit for it to be considered safe?    The 30% limit (9mA in this case) of 531.3.2?
Question 2:
How should I proceed to be sure of resolving the problem, and in a cost-effective way?
  1. Change the consumer unit for a split load dual RCD configuration – with careful assignment of the circuits each RCD will carry roughly 8.5mA of standing earth leakage, but will this give immunity to further tripping, maybe a three-way split required?
  • Change the consumer unit to all-RCBOs – this is expensive for the customer and I can’t give a 100% guarantee that the tripping will cease… how much earth leakage could a mains-borne transient or fault cause?  It has the benefit that, if I have missed a circuit fault, it will be isolated by an RCBO when it next occurs.
  • Get the DNO to check the overhead cable before changing the consumer unit.  Will they do that?
  • Chase down and reduce the earth leakage current?  Would you consider this a “faulty” installation?
  • Any other ideas?
Any thoughts will be gratefully received, and I’ll be sure to let you know how it goes.
  • It appears we had the options of "non BASEC", BASEC approved to 600 megohm and BASEC approved to 2,500 megohm with prices reflecting this.
    Indeed - I believe that while a manufacturer could legitimately produce both "approved" and "non-approved" versions, if they did produce both the non-approved version had to be clearly labelled as such - some years ago during renovation works I found this under the floorboards:
    I take the points that (i) I can’t issue an EIC with the Test Results showing insulation resistance failures on three circuits and (ii) there shouldn’t be any significant leakage from the fixed wiring in this installation – it’s all PVC, I haven’t seen any rubber or mineral insulated cable.
    I can see that I need to confirm my insulation resistance test results (the identical 67k values on two circuits do look fishy) and then trace the faults and also, that changing to an RCBO board is OK to avoid the whole installation tripping due to excess leakage in the loads (coupled with line-side effects etc) but not to provide tolerance of faults in the fixed wiring.
    With the faults fixed there may a reduced incidence of the RCD tripping and the immediate need to replace the consumer unit could be re-evaluated – although re-positioning it would be an improvement,  there is indeed nothing stopping it from getting kicked, it’s not in cupboard and the cover is missing.   There may also be the option to de-install the over-the-house conduit which I can well imagine was justified as a short-term solution as it’s inconsistent with the skill involved in tracing the fault and the diligently labelled disconnected cables.
    Thanks all, hopefully the next instalment will be the last!
    GrahamJ
  • mapj1:
    But it matters not one jot.
    It does ?, as one who started out on the 13th edition. Also installed the stuff including preparing the ends for termination, the outer braiding was merely for abrasive protection, it was not insulating per se, it had to be dressed back ½ inch to avoid creepage at the ends - the insulating property was the Vulcanised Rubber for the core! ?  .
    jaymack