Multicore cables (YY but not PVC/PVC)
I wonder if I could previal for some learned opinions.
We undertake installations of stage lighting amongst other things, and often use a 19-core 'YY' type cable (though it isn't really YY as the insualtion and sheathing is not PVC/PVC - it is a LSF variant) for links between switched power units or dimmers and internally wired lighting bars.
We have undertaken many such installations, and we are registered with the NICEIC who have audited and inspeced many such installations and passed them.  We have also raised specific questions with them on the use of the cable and we get varying answers.  They are never willing to give an emphatic 'yes', but neither do they say 'no'.
As I understand it - there is not a relevant construction standard that covers this type of cable construction, so it can't comply with a standard that doesn't exist.  There are however many standards (many of which form normative references for construction standards of other cable types) with which it does conform.  These include EN 50525-1 (General requirements) EN 60228 (conductors) and various fire performance standards (EN 50575, EN 60754, EN 60134 and EN 60332).  We also know that the insualtion and sheathing material is standards-compliant and is commonly used in cable manufature.
We are embroiled in a dispute with a main contractor who is claiming the installation is non-compliant as the cable does not meet a construction standard. Reg 511.2 allows for use of euipment not covered by a Britsh or Harmonised standard if the designer/specifier confirms that the equipment provides at least the same degree of safety.  This cable is covered by multiple standards but not a single 'construction' standard that is applicable to this type
We have undertaken what we believe to be a thorough assessment of this cable which is attached here:  Assessment of Cable NILTOX LF 319.docx
The use of the cable is noted on the certificate and the assessment and supporting documentation from the supplier is attached, but the main contractor is still refusing to accept this route.
So a couple of questions for the learned community:
  1. Have we missed anything in our assessment, or does it seem thorough and complete?
  • Should the use of this cable be recorded as a 'departure' (our agument is that we have complied with 511.2 and therefore it is not a departure) or just recorded as a note?
Thanks in advance.  Happy to answer any further questions.
Jason.
  • Well, Wierdbeard, that is a point of view but in reality, I think that doesn't matter. The point is that the wiring is fixed as an installation, and despite BS7671 feature creep, has always been covered. Appliances usually have a plug, although sometimes it is better to wire them directly to the installation, like a cooker or immersion heater. A few, like smart controllers, are not plugged in and continue the fixed wiring, so should be covered by the definition, like downlighters with an external transformer. Whether the speaker wiring to your Hi-Fi is covered is a moot point, but the amplifier plugs in (usually) so is the appliance along with the speakers.  Simplistic I know, but usually, this works. The lighting installation is fixed, I asked very carefully about plugs and sockets, and the answer fits the above definition very well.
  • David, that is the point. Apologies I might have been a bit cryptic in my response.
    So, the dimmer is a type of controlgear, the wiring downstream of it is fixed at least to a point.
    If we say that wiring systems stop at connectors, cable couplers, or a control device, in a smart home there might not be much left of the fixed installation otherwise.
    I think it's also OK to say that fixed appliances or equipment that connect to via plug and socket-outlet are also part of the fixed installation. A good example are data centre racks, which have additional connections for earthing which are "hard wired", but the mains might connect via plug and socket-outlet.