UKPN:
Height of Line Conductors:
Not exceeding 33,000 volts 5.2 metres
Exceeding 33,000 volts, not exceeding 66,000 volts, 6 metres.
Exceeding 66,000 volts, not exceeding 132,000 volts, 6.7 metres.
Exceeding 132,000 volts, not exceeding 275,000 volts, 7 metres.
Exceeding 275,000 volts, 7.3 metres.
For those interested, UK Power Networks takes energy from National grid at 400kv at a Grid supply point (a substation) and steps it down to 132kv for distribution locally.
Regards, UKPN
In addition to the heights of the line conductors I also want to know the minimum distance that has to be maintained from the base of pylon/tower to any nearest residential plot limit of the development in which the developer wants to build residential towers.
Mind you not all pylons / towers near houses actually are EHV.
this and this are opposite ends of the same span - the really small (all things relative...) insulators tell us it is not as EHV as we think, just made up extra tall to get up and over the housing estate. They do not buzz like the higher voltage cousins.
Mind you , I have no idea how common that sort of trick is.
Mike.
Similarly this is only 33 kV as evidenced by both the insulators and the 1950s signage. Drops down to wooden poles a mile or two away here. It would in fact appear to interconnect with the one you mentioned.
I'm unsure if there was an intention to upgrade it later, the pylons would appear to be designed to allow either the 6 cables to be much more widely spaced than they currently are, or perhaps to double-up to four 33 kV circuits. Who knows.