Hi all, just looked and the builder is not telling me the right details. The cooker line is actually a 6mm. Is this able to run a 7.2kw induction hob and 5kw cooker on a 45A mcd? Thanks
To have proper overload protection (rather than relying totally on diversity) the cable need to have a rating at least that of the MCB. Cable rating vary depending on how they're installed - 6mm² is only good for 45A if clipped direct or equivalent (e,g. embedded in plaster) or in free air - if it's run in other ways - e.g. in building voids or worse through thermally insulating material it'll be shy of that.
The obvious solution is just replace the MCB with a 32A one.