P.M.E. and a Broken Neutral.

Nowt ont box? Then try this to challenge the mind.

Podcast 77: Earthing pt 3, Hazards and Neutral Current Diversion - Bing video


Z.
  • Thanks Mike


    That is the vehicle charging video could you put up the PME video.


    JP
  • When I clicked on it I got the electric vehicle charging one too thought was me doing sumthing wrong gladits not my error


  • https://youtu.be/tlzuifWzaCM


      - Andy.
  • Looking forward to the pme video.

    Now UKPN's network is assumed to be pme Does this mean that where once  Ze on TN S was 0.8  Do we now assume 0.35. ?
  • I just watched the video and its now a lot clearer in my mind about the dangers of PME im really starting to think it was a bad idea I know earthing the neutral is by and large a good thing BUT only if a system is well maintained
  • Thanks Zoom for allowing the little divert into Quarries from your post.

    Thanks Andy for pointing out PMB can  have theoretically two different ways of connecting to ground earth.

    Thanks John, I have now viewed the prod cast on earthing, and the panel of experts very good.

    regards 

    jcm