TPN boards, even where they do comply with BS EN 61439-3 can't be described in BS 7671 as consumer unit simply because BS 7671's definition of a consumer unit only applies to single phase equipment (i.e. having DP incomer).
As I read it, 421.1.201 isn't saying that the requirement for non-combustibility applies to BS EN 61439-3 equipment - rather it's saying that where ordinary persons are about (domestics) then it must both comply with BS EN 61439 as well as having an non-combustible enclosure - the BS EN 61439-3 is part of the requirement rather than part of the condition.
If a householder is following instructions to 'turn off at the main switch' surely the switchfuse is exactly the place they should be doing it. So really I don't buy that the existence of a downstream CU means that the householder wouldn't have any cause to operate the switchfuse.
I didn't know about the 63A limit for outgoing ways for CUs - and am a little surprised about that - since the BSI site in the overview of BS EN 61439-3 says rated current (Inc) of the outgoing circuits does not exceed 125 A and the rated current (InA) of the DBO does not exceed 250 A"
and some examples of 80A/100A switchfuses appear to claim some sort of compliance with BS EN 61439-3 as well as 60947-3.
I'm still struggling to see why a 3x12 way TPN DB with 125A incomer and perhaps several 63A outgoing MCB is considered to be similar to a CU, but a 1-way SP distribution board with a 100A incomer and a 63A outgoing fuse isn't.
Fortunately building regs have their own definitions of things (and often didn't align with BS 7671 ones anyway) - as far as I can tell the notification requirement applies only to consumer units (not similar switchgear) - so perhaps there's no need to notify a TPN board replacement in a domestic?
Presumably something with a lot of high current terminal connections is, purely on probabilistic grounds, more like to to go whoosh than a FCU or fuse switch.
A few.
One is called a consumer unit as it is done to a standard where it is intended for use by ordinary persons, but it's also the application; is that the only consumers equipment?
DBOs [ consumer units] to BSEN 61439-3 are limited to 63 amp per way; note your example is 45 amp, also it is pre 61439-3, but I get the gist. KMFs and switch fuses can have HRC up to 80 amp /100 amp respectively. The KMF/switchfuse devices usually serve a full blown consumer unit to BSEN 61439-3, in that instance it is clear the consumer unit is the thing intended for use by an ordinary person.
Those are the essential differences, but there are other things beyond BS7671 and the clumsy wording of 421.1.201,
like the Building regs and particular requirements for dwellings.
421.1.201 is only “what shall comply with 61439-3”. Firstly it is "consumer units". In my opinion the "similar switchgear" was to cover the potential use of TPN DBs for a 3 phase domestic or converted to single phase for lots of ways; it becomes a DBO when used in a domestic, most are now 61439-3 anyhow, but when the reg was published, some TPN distribution boards were not manufactured as DBOs. The Consumer Unit is specifically intended for use by ordinary persons, a DBO. Also the similar bit is for self assembled consumer units where you purchase an enclosure separately and the devices separately. I will go with a consumer unit like enclosure with a main switch with one or more ways/MCB’s that you can re-arrange yourself to not escape being 61439-3. But we have to be careful what we attribute “similar switchgear” to. It could lead to a bit of a conflict with notification requirements for building regs.
Replacing a 800KMF with a new one is not notifiable works because it is not a consumer unit.
So an SFCU?
UKPN:
"I am not interested in the DNO view"
You should be, because without a competency certificate signed by a DNO you are not able to work live on their equipment.
An unauthorised "isolator" is not covered by the suppliers insurance.
The fitting of an unauthorised "isolator" will loosen the meter tails irrespective of a withdrawn fuse so the meter terminals will have to be checked afterwards. This of course requires seals to be broken and replaced, again only persons with a competency certificate are able to do this.
Your best course is to request a suppliers isolator via the customer. The suppliers meter operator will attend, fit, and you being there at the same time can reconnect the tails.
Ascertaining whether a plastic isolator/sw/fuse is allowable under the "wiring regulations" would be futile anyway because that question has been thrown around for years and no one from the "institution has stuck their head above the parapet and given a definitive answer.
Regards, UKPN.
The DNO will be attending. The supply is being moved because of an extension and i have to extend the tails longer than 3 meters. The box will be supplied and fitted by myself with switch fuse and tails already fitted for a changeover on the day. As i said in the OP the DNO guys round here are always very obliging and helpful. The boxes are tight but they don't need to fit their isolator if i have fitted one already.
Gary
perspicacious:
I reckon that both are my boxes on my land. My land! So where is the legal basis for the DNO "owning" one of them?
On that logic, you own the DNO service cable, cut-out and meter Chris!
As Simon Barker says, the householder (or builder) has to supply (and if necessary, replace) the boxes. It is, of course, a condition of the supply contract that the DNO and supplier may install their tackle in my box, on the garage wall, and in my ground; but that doesn't mean that they own the box or the space within.