Presumably something with a lot of high current terminal connections is, purely on probabilistic grounds, more like to to go whoosh than a FCU or fuse switch.
TPN boards, even where they do comply with BS EN 61439-3 can't be described in BS 7671 as consumer unit simply because BS 7671's definition of a consumer unit only applies to single phase equipment (i.e. having DP incomer).
As I read it, 421.1.201 isn't saying that the requirement for non-combustibility applies to BS EN 61439-3 equipment - rather it's saying that where ordinary persons are about (domestics) then it must both comply with BS EN 61439 as well as having an non-combustible enclosure - the BS EN 61439-3 is part of the requirement rather than part of the condition.
If a householder is following instructions to 'turn off at the main switch' surely the switchfuse is exactly the place they should be doing it. So really I don't buy that the existence of a downstream CU means that the householder wouldn't have any cause to operate the switchfuse.
I didn't know about the 63A limit for outgoing ways for CUs - and am a little surprised about that - since the BSI site in the overview of BS EN 61439-3 says rated current (Inc) of the outgoing circuits does not exceed 125 A and the rated current (InA) of the DBO does not exceed 250 A"
and some examples of 80A/100A switchfuses appear to claim some sort of compliance with BS EN 61439-3 as well as 60947-3.
I'm still struggling to see why a 3x12 way TPN DB with 125A incomer and perhaps several 63A outgoing MCB is considered to be similar to a CU, but a 1-way SP distribution board with a 100A incomer and a 63A outgoing fuse isn't.
Fortunately building regs have their own definitions of things (and often didn't align with BS 7671 ones anyway) - as far as I can tell the notification requirement applies only to consumer units (not similar switchgear) - so perhaps there's no need to notify a TPN board replacement in a domestic?
gkenyon:
It could also be argued that an enclosure containing a single RCD, say for a shower, is not "similar switchgear" as it does not include for "distribution", it's a dedicated device (similar, the SRCD).
So is a switch-fuse (+/- RCD) at the supply end of a distribution circuit distributing leccy or not?
perspicacious:
Can i fit a plastic switch fuse such as an 800kmf in the external meter box or does it have to be metal.
So it wasn't really a question.
The box will be supplied and fitted by myself with switch fuse and tails already fitted for a changeover on the day. As i said in the OP the DNO guys round here are always very obliging and helpful. The boxes are tight but they don't need to fit their isolator if i have fitted one already.
Regards
BOD
So how did you come to that conclusion ? ?
It is raining......
The consumer unit will have things that are in the off position if there is a fault or overload. That is consumer friendly, hence the moniker consumer unit for domestic [household] premises.
Of course, a 1 way SPN distribution board is "similar switchgear"
I do not think we should be condemning the use of KMFs in domestic installations. There are many, many thousands installed, they are compact and manufactured as a switchfuse, usually for a specific purpose where a distribution board is not suitable.
AJJewsbury:
BS 7671's requirement for a main switch (or main circuit breaker) is that it is as near as practical to the origin of the installation (462.1.201) - which is just what you want if you cut off power to the entire premises for whatever reason - so I still say (unless one is provided by the DNO) the the switch on a switchfuse should be used in preference to one on a downstream CU - especially by ordinary persons who are less likely to understand the distinction and/or be aware exactly where the submain cable runs for example.
I agree - and if it's the type where the fuse is easily accessible, take out the fuse and put it in your pocket. So is this now the main switch, and are you going to label it as such?
So isn't a swithfuse just one example of a 1-way distribution board? They might (or might not) comply with different standards - but BS 7671 doesn't define things in terms of which standards they are constructed to meet, but in terms of their fundamental components and functionality. If it's "an assembly containing switching or protective devices ... associated with one or more outgoing circuits fed from one or more incoming circuits ... " BS 7671 seems to consider it a distribution board.
Now there I've got to differ - Consumer Unit got their name back in the day when rewireable fuses were still king - 'trip switches' (MCBs etc) are just the current fashion. We may well be returning to the situation were consumers may have to pull out and replace bits of their CUs to keep their installation in a serviceable condition if the current fad for SPDs (with replaceable cartridges) continues too.
BS 7671's requirement for a main switch (or main circuit breaker) is that it is as near as practical to the origin of the installation (462.1.201) - which is just what you want if you cut off power to the entire premises for whatever reason - so I still say (unless one is provided by the DNO) the the switch on a switchfuse should be used in preference to one on a downstream CU - especially by ordinary persons who are less likely to understand the distinction and/or be aware exactly where the submain cable runs for example.